Anonymous Poster #1

CT Rating

06/11/2012 4:18 AM

the incomer MCCB rating is 100A. there is a requirement for Ammeter and voltmeter. The CT for the ammeter used has to be 20VA as per the client requirement. i have used a CT 150/1A 20VA CT. even 100/1A CT is available but it is of long delivery, bigger in dimension & expensive than 150/1A CT. CT type is RT (indoor type in Air). make is ITL (UK). my question is whether this kinda connection breaches any international standards ? Please Explain me how I can explain my client technically that it is acceptable to use 150/1A CT instead of 100/1A CT.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster #2
#1

Re: CT Rating

06/11/2012 7:15 AM

actually you can use 100 a kw meter without needing to CT even 3 phase or single phase

Reply Off Topic (Score 7)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: CT Rating

06/11/2012 8:10 AM

Just put a bit of tape on the meter. Divide by 66.6%

Problem solved!

__________________
The reports of my death are greatly exaggerated.
Reply
Associate

Join Date: Jul 2011
Posts: 48
Good Answers: 1
#3

Re: CT Rating

06/11/2012 11:24 AM

What accuracy class is the CT, if it's a high accuracy one, and you have set the meter to 150/1 to match the CT it's really not going to make any difference.

Are they analogue meters? seems a very high VA rating requirement for a digital meter

Reply
Anonymous Poster #1
#4
In reply to #3

Re: CT Rating

06/12/2012 5:01 AM

Accuracy Class1.

Yes, they are analogue meters.

High VA rating because The CT provided for Ammeter in the distribution board is also used for current indication to SCMS (Substation Control & Monitoring System)

Reply