Delta-Wye Transformer Neutral Earth

06/11/2012 7:12 PM

There is delta-wye transformer(480V/208V) to be used for lighting fittings with 3phase-4wires. The neutral in 2nd winding is solid earthed to the hull. I am wondering how this earthing conductor is sized. Is there differrent principles between IEC and NEC. I couldn't find principle.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Delta-Wye Transformer Neutral Earth

06/11/2012 9:41 PM

For circuit using 16mm sq and below, earth shall be the same as live conductor size... while 16mm to 35mm sq, the earth cable shall be 16mm, anything above 35mm sq, the earth cable shall be at least 1/2 the size of the live conductor... IEEE Wiring Regulation...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#2

Re: Delta-Wye Transformer Neutral Earth

06/12/2012 12:25 AM

There is a NEC table giving sizes of ground wire for each size(Amp)of CB. Which one you want to follow IEE(BS) or NEC?.

__________________
pnaban
Register to Reply
Member

Join Date: Jun 2012
Posts: 6
#3
In reply to #2

Re: Delta-Wye Transformer Neutral Earth

06/12/2012 6:22 PM

Please advise based on IEE.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4
In reply to #3

Re: Delta-Wye Transformer Neutral Earth

06/12/2012 10:48 PM

Solareagle has given it.