Switchgear 400V vs 3.3kV

06/11/2012 11:41 PM

Project I am working, one of the client's document states any motor rating more than 150kW shall be fed from 3.3kV. We have not considered any 3.3kV in our design by now, we only have 400V switchgear.

I want to convince client to use 400V for 220kW motor. Please advice how can I convince client to use 400V instead of 3.3kV.

Register to Reply
Pathfinder Tags: Switchgear 400V vs 3.3kV
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Switchgear 400V vs 3.3kV

06/11/2012 11:54 PM

Try a cost comparison, for one.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Switchgear 400V vs 3.3kV

06/12/2012 12:59 AM

Present a convincing argument. You know the circumstances of the installation, right? Why do you think it is better for the client?

Or, are you in marketing?

Register to Reply
Member

Join Date: Jan 2012
Posts: 9
#3

Re: Switchgear 400V vs 3.3kV

06/12/2012 1:46 AM

same kind of system is exisitng at site means 220kW from 3.3kV thats why i am finding difficulty in convincing. Budget is not a issue with client and i am not in marketing.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: Switchgear 400V vs 3.3kV

06/12/2012 3:13 AM

If budget is not an issue, provide the Client with what he is prepared to pay for. Redevelop the scheme with components at 3.3kV, and be done with it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Switchgear 400V vs 3.3kV

06/12/2012 3:24 AM

What if there is only one motor > 150kW? Does he then want to run a separate 3.3kV service for it, or a step-up transformer?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Jan 2012
Posts: 9
#6

Re: Switchgear 400V vs 3.3kV

06/12/2012 4:07 AM

There are 4 motors of 220kW.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: Switchgear 400V vs 3.3kV

06/12/2012 4:09 AM

3.3kV is sounding better as the information in this thread continues to be uncovered.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
5
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: Switchgear 400V vs 3.3kV

06/12/2012 10:22 AM

Benefits of 3.3kV:

Less copper, smaller transformers, lower i^2R losses, lower operating costs.

Disadvantages of 3.3kV:

Higher initial cost (capitalization), less availability of repair parts, you are not comfortable with it.

Benefits of 400V:

Lower capitalization, more readily available replacement parts, you are familiar.

Disadvantages of 400V:

More losses, lower system efficiency, thus higher long term cost of ownership.

On average, studies have shown that the higher capitalization to go with MV motor control is wiped out in approximately 5 years of lower operation costs. That is often not a good enough payback period for purist accountants, but considering that large motors are usually the heart and soul of a plant production system, most managers will consider the longer term benefits. That pretty much damages your predisposition I know, but the truth is the truth.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 5)
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#9

Re: Switchgear 400V vs 3.3kV

06/12/2012 10:29 AM

If you only have 440V gear it looks like the customer has picked the contractor.

If you can't give the customer what he wants then what use are you?

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 2)
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#10

Re: Switchgear 400V vs 3.3kV

06/12/2012 12:47 PM

What about the arc flash considerations? I would think the higher voltage would represent significantly higher damage potential in an arc flash.

This point of view might give you more credibility if safety is important. Just don't over emphasize the point.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
3
Power-User

Join Date: Jun 2009
Posts: 134
Good Answers: 11
#11

Re: Switchgear 400V vs 3.3kV

06/12/2012 2:27 PM

"we only have 400V switchgear"

You came to the wrong place for advice.

The people here will give you advice on the best technical solution, not on how to sell the solution that is best for you.

Register to Reply Good Answer (Score 3)
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#15
In reply to #11

Re: Switchgear 400V vs 3.3kV

06/13/2012 12:56 AM

I can only assume that YOU read the Client's specifications BEFORE you decided to take on this project.

As soon as you took on this program, YOU committed to provide THEM with what they wanted. IF you cannot meet this criteria, WHY DID YOU BID IT?

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply Score 1 for Good Answer
Commentator

Join Date: May 2011
Location: Brisbane, Australia
Posts: 62
Good Answers: 3
#12

Re: Switchgear 400V vs 3.3kV

06/12/2012 10:32 PM

RULE #1 The Client is always right

If in doubt refer to RULE #1

Register to Reply
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#17
In reply to #12

Re: Switchgear 400V vs 3.3kV

06/13/2012 5:26 AM

The client is always right..... but there are times when you can point out how the client can be more right than he is now.

3.3kV will require extra certification for the client's maintenance personnel. If they are already working on 3.3kV no problem, if not "High Tension" trained electricians come at premium prices and are not easy to find. (Comment based on UK experience)

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#22
In reply to #17

Re: Switchgear 400V vs 3.3kV

06/18/2012 4:34 AM

That's the Client's problem, not the Original Poster's.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Jan 2012
Posts: 9
#13

Re: Switchgear 400V vs 3.3kV

06/12/2012 10:51 PM

Thanks for all the responses.........seems no escape from 3.3kV system.

Register to Reply
Active Contributor

Join Date: Jan 2012
Posts: 16
#14
In reply to #13

Re: Switchgear 400V vs 3.3kV

06/13/2012 12:52 AM

Dear Spiki,

Surely your 4 nos. of 220kW motors are driving some applications....conveyors, pumps, blowers whatever. There may be a solution. Talk to your Mechanical Counterpart/Process designer.........tell him your your problem, your considerations and how the incorporation of a new 3.3kV Switchboard along with all associated equipments, protections etc. would affect your budget and the entire project as a whole (hopefully you are in EPC business). And finally request him to reduce the motor ratings by redisigning. This is very much possible and often done.

e.g I am assuming arbitrary figures. say a conveyor has a BKW (actual power requirment to drive the conveyor) of 200kW. There are 2 options with the designer. Either he can choose 1 no. 220kW motor (considering all margins and then standard rating); or; alternatively he can design his system with 2 nos. 150kW motors to drive his equipment. His outlook/matter of concern is not the motor rating or HT/LT volatge level. He is only concerned with the availability of the required BKW at his driving end to drive his equipment. However in the later case both the motors will have to run simultaneously to drive the conveyor. This principle can also be applied to achieve a desired flow rate (considering applications otherh than conveying)

Talk to your mechanical/proces designer. If you can take him in confidence, you are done. BEST OF LUCK.

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#16

Re: Switchgear 400V vs 3.3kV

06/13/2012 4:14 AM

We used to swap from 415 to 3.3kV at 90kW.

The impact of starting and loading 220kW drives onto an LV system is enormous and not desireable.

Long before you try and convince the client he wants to run his motors at 415V I think you need to do a load study. Find out what the fault currents are, find out what the implications are on the system of swapping voltages.

My guess is you have completely underestimated the impact these drives will have on your network.

If there is distance between the MCC and the motor consider the amount of copper you are going to have put into the ground.

If you haven't done a study doing a tool such as SKM power tools or similar its time to stop and hand this over to an electrical engineer. I'm not convinced you understand the potential problems.

Register to Reply Score 1 for Good Answer
Anonymous Poster #1
#18

Re: Switchgear 400V vs 3.3kV

06/13/2012 8:00 AM

I am not sure how big is this industrial facility? Utility coordination is certainly required for additional 880 kw on their system. Utility Co may not allow 4x220 kw motors to run on 400v system voltage. In order to avoid voltage flucatations and 415v system stability, these motors shall run thru step-up 3.3kv XFMR.

Register to Reply Off Topic (Score 7)
Active Contributor

Join Date: Jun 2012
Posts: 10
Good Answers: 1
#19

Re: Switchgear 400V vs 3.3kV

06/13/2012 8:46 AM

Spikenet, I have 3 questions:

1- Is there 3.3KV switchgear running existing equipment at this site?

2- How big is the 400V transformer feeding the existing MCC you want to use and is there 880KW of extra capacity in the transformer and MCC?

3- Who designed these upgrades, is the design done?

I am wondering if you will really save any money by using 400V motors and If the client already has 3.3KV equipment you can't use the maintenance training argument.

As long as the lead time fits in your schedule the 3.3KV design will work better for the client. Just make sure to use the proper cable terminations. Some say the kits are not required below 6.9KV but for the price I think it is worth it.

Good planning = Good luck

Register to Reply
Member

Join Date: Jan 2012
Posts: 9
#20

Re: Switchgear 400V vs 3.3kV

06/13/2012 8:56 AM

Frankdolan yes 3.3kV is exisiting at site. As we have gone ahead in design with only 400V (involvement of vendor & all) ie why i was thinking to have a session with client to convince them to run 230kW from 400V. but seeing all the responses i have decided to include 3.3kV in design.

Thanks everyone for active contribution.

Register to Reply
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#21

Re: Switchgear 400V vs 3.3kV

06/13/2012 9:00 AM

One reason for using 3.3KV equipment is to keep the motor physical size, motor supply cable/wiring physical size, and the switchgear physical size much smaller and thereby require less space for the equipment installation.

Another reason is to keep maintenance costs lower due to: less mobile equipment, smaller equipment, and fewer personnel being required to facilitate removal and/or movement of the motors when they fail. (And they will fail.)

While the initial installation costs are somewhat comparable, the long term maintenance costs are significantly higher for the lower voltage equipment in the higher horsepower/KW range.

I doubt you will be able to convince the client to change their mind but good luck.

Register to Reply
Register to Reply 22 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Carl Pugh (1); energygod (1); frankdolan (1); gckent (1); jhhassociates (1); JRaef (1); kolokol (1); lyn (1); NotUrOrdinaryJoe (1); PWSlack (3); SHOCKISCAN (1); silverfox (1); spikenet (4); TonyS (1); Tornado (2)