We have an induction motor 11 kV ABB motor AMD710L2TBSBM the cooling fan motor filter very dirty and full of dust, we want to clean the cooling motor fan filter with water, can anybody give comment?it is correct method or not? or maybe the filter will damage or develop some sludge?please help me
Re: MV motor cooling fan filter cleaning
06/19/2012 11:35 AM
Depends what the filter is made of.
Metal/plastic/paper/fabric?
Have you looked at the manual?
Do you have a manual?
Have you contacted the supplier?
Have you done anything?
A little information from you will help.
Otherwise no way.
Re: MV Motor Cooling Fan Filter Cleaning
06/19/2012 11:47 AM
Here you are, my good sir:
The Manual!
Chapter 7 in particular was pretty useful looking for you. In the future, the manufacturers website typically has .pdf's like these readily available for you to look at. If they don't, a quick phone call will often times result in either a straight answer from their technical support, or some sort of digital / physical copy of the manual sent to you.
Good luck!
The first law of thermodynamics is you do NOT talk about thermodynamics.
Reply Good Answer (Score 6)
06/19/2012 1:05 PM
You are too kind.
06/19/2012 5:21 PM
An excellent find, and a good share. Well done!
06/19/2012 9:40 PM
"The filters should be cleaned regularly. The cleaning interval depends on the cleanliness of the
air in the surrounding environment. The filters have to be cleaned when the temperature
detectors in the winding show abnormal temperature or approach the alarm level.
If a filter differential pressure monitoring system is being used, the filters should be changed
immediately after a pressure alarm. The alarm level is such that 50% of the air filter surface is
obstructed. The operating personnel should also manually inspect the filters frequently.
Remove the air filters for cleaning. If the surrounding air is sufficiently clean, the filters can be
changed during operation. They should regularly be cleaned by vacuuming first from the
upstream side, then on the discharge side. Periodically, a thorough wash with clean water is
recommended to release any dirt not removed by vacuuming. When heavy grease
concentrations are encountered, the filters should be washed with a detergent solution. This
solution should be rinsed thoroughly before returning the filter to service. Be careful to install
the air filters in the correct direction, i.e. the arrows on the air filter frame indicate the direction
of airflow. Some filters can be installed in either direction. Refer also to the air filter
manufacturer information."
Good Answers: 39
06/20/2012 12:36 AM
I get the impression that you're possibly wanting to wash the filters in place. That would be a bad idea. The mud generated would coat the windings and make them overheat. Pull the filters, wash them with mild detergent and hot water, so the dirt goes out from the inside of the filter to the intake side. Dry well before replacing. Buy spares if you need to run the motors during the cleaning process.
Align culture with nature...