Harmonic Block

06/20/2012 11:57 PM

A 200 MVA transformer's trip bloked during differentilal trip due to 2nd harmonic. It is observed that harmonic content during fault is above 45%. So how can I ovecome this problem. The relay is MICOM 631.

Please advise

Register to Reply
Pathfinder Tags: differential harmonic
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#1

Re: Harmonic Block

06/21/2012 12:12 PM

Hello byj,

Perhaps you have gotten started in the wrong direction. The second harmonic should not be a consideration unless you lost a phase and your instrumentation has misinterpreted the event.

Make sure you are connected as directed by the manual.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Power-User

Join Date: Jun 2010
Location: Canada
Posts: 139
Good Answers: 6
#2

Re: Harmonic Block

06/21/2012 10:40 PM

Your explanation of the situation you are in - is totally inadequate.

Was this a "through-fault" ? Or did the transformer fail ??

The harmonic content of faults varies far and wide . . . NO it is NOT 45%.

Second harmonic is caused only by a saturating transformer, typically present when a transformer is energized. The presence of second harmonic is always restraining the tripping.

Register to Reply
Commentator

Join Date: Mar 2009
Posts: 57
#6
In reply to #2

Re: Harmonic Block

07/15/2012 12:11 AM

Fault is at OLTC

OLTC damaged

The waveform shows 2nd harmonic content above 49%

how it happened ???

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#7
In reply to #6

Re: Harmonic Block

07/15/2012 6:03 AM

how it happened ???

you asking about the damage or the harmonic?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#3

Re: Harmonic Block

06/22/2012 6:58 AM

2nd harmonic block is a standard feature of all transformer differential relays and is intended to give stability to the protection during energisation.

The transformer inrush current is rich in 2nd harmonics and that is the reason the 2nd harmonic threshold is used to differentiate inrush from faults.

It is true that this may prevent protection operation when transformer fault were to coincide with the energisation.

But, will the 2nd harmonics be dominant if the fault were to be in the transformer!! I am not sure. It will help if you can detail the problem a little more.

__________________
Raghunath
Register to Reply
Commentator

Join Date: Mar 2009
Posts: 57
#4
In reply to #3

Harmonic Block

06/22/2012 3:12 PM

200 MVA , 220KV/110KV Transformer - independent units

Y-phase OLTC failed

Bucholz, PRV acted.

But differential trip blocked by harmonic

We analysed the waveform and observed that 2nd harmonic contect exceeded above 45%.

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#5
In reply to #4

Re: Harmonic Block

07/06/2012 8:31 AM

It appears the failure occur at the time of energisation. Is that true, byjuram!!

__________________
Raghunath
Register to Reply