Transformer Fuses

06/21/2012 2:09 AM

Hi,
Is transformer LV fuse supposed to operate first than HV fuse?
Regards,sks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: transformer fuses.

06/21/2012 2:24 AM

That would be desirable, but I'm not sure whether it is required (which could vary by local Codes).

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Dec 2009
Posts: 247
#2
In reply to #1

Re: transformer fuses.

06/21/2012 2:37 AM

thanks,

i am considering a fault on LV side. Should a LV fuse operate for fault on HV side as well?

Regards,

sks

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #2

Re: transformer fuses.

06/21/2012 4:14 AM

No.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - New Member Technical Fields - Technical Writing - New Member Technical Fields - Education - New Member Fans of Old Computers - Apple II -

Join Date: Sep 2011
Location: Bellingham, WA
Posts: 191
Good Answers: 46
#6
In reply to #2

Re: transformer fuses.

06/24/2012 9:29 AM

Fuses protect against excessive current. The only way a fuse will operate ("blow") is if the current through it is too great, for too long. If a transformer suffers a fault in its primary widing, this will cause excessive current on the primary (HV) side, but not on the secondary (LV) side. A fault in the secondary circuit, however, will cause current to increase for both the primary and secondary windings.

__________________
They call me "lightning" when wielding a hammer, because I never strike twice in the same place
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 171
Good Answers: 1
#3

Re: transformer fuses.

06/21/2012 3:35 AM
Register to Reply
2
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#5

Re: Transformer Fuses

06/21/2012 8:33 AM

The protection in electrical systems are always graded. As far as possible the first protection whether it is fuse or breaker nearest to the fault must operate first to avoid the healthy circuits not to get affected by a fault on defective circuit. In case of failure of the nearest protective system with in the rated time the next above fuse or breaker should operate. The proper grading is essential to avoid undesired power outage at the same time provide proper protection to the system and life . So the LV fuse have to be defined to operate first before the fault current trips the transformer. In practical at times the transformer trips first in case of earth fault and short circuit because they are designed more sensitive and are very prompt in operation to avoid fire or accidents in line even if the LT protection fails.

Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Aug 2009
Posts: 11
#7

Re: Transformer Fuses

06/26/2012 9:07 AM

If the fault is on the HV side, then the HV fuse blows: if on the LV, then the LV fuse. The idea is to isolate the transformer from the fault circuit. In the event of error (failure of fuse to blow)- then yes, a through fault on the HV side may cause the LV fuse to operate to take out the load.

__________________
A wise man didn't become wise over night.
Register to Reply
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

nobodysomebody47 (1); PWSlack (1); sauravbabu (1); simbarashe gunzvenzve (1); tonykuphaldt (1); Tornado (1); V.I.Abraham (1)

Previous in Forum: Harmonic Block   Next in Forum: 3 Phase Motor Rotates

Advertisement