Problem in Current Transformer

06/23/2012 10:17 AM

when we are conducting relay testing by giving primary injection test to the current transformer .thr relay is not operate & also the CT circuit does not show any current in primary as well as in secondary side what is the probable cause. is the secondary circuit open or the CT core has gone out of order .But when i check the secondary circuit it stood ok. is the cause of wrong wiring viz. changing of CT S1 & S2 connection or any other problem

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: problem in current transformer

06/23/2012 10:58 AM

If you have as such basic questions, I really don't think you should be working with CT's.

If the primary isn't conducting, there's the first place to look. Changing the secondary around isn't going to help.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 3)
Participant

Join Date: Dec 2011
Posts: 4
#2

Re: Problem in Current Transformer

06/24/2012 5:26 AM

When doing primary injection , the current is not dependent on the CT or secondary of CT. So there must be a problem with the current injection tester. You must be able to read the current injected on the tester. Also note that the primary current injected is much higher than what you normally inject with secondary current injection.

Also you must be specific while you are explaining a problem. The type of relay, settings, CTs, CT ratio and current injected must be clearly mentioned so that the problem can be analysed properly

Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#3

Re: Problem in Current Transformer

06/25/2012 9:29 AM

Dear Sehdev,

Have you checked proper functioning of your Primary Injection test set? First check the above. If it is found O.K. then pl. check the primary circuit (continuity test ) of the CT.; you have not mention the type of the CT(i.e bar primary or wound primary)

Hope this may help you.

Manindra

__________________
Manindra
Register to Reply
Anonymous Poster #1
#4

Re: Problem in Current Transformer

07/12/2012 8:57 AM

Hi there,

Put a short on your secondary circuit right at the CT....send current again and test with a clippon for some current.....if you get current then start looking for the fault in your secondary circuit..........if you get no current then your CT is damaged

Cheers

Mike

Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Kiscal (1); manindra (1); TonyS (1)