Can I Get A Contactor Without Connecting the Neutral Side? (A2)

06/23/2012 11:44 AM

Hey all

Just basic but for the current to flow it has form a loop right. So If I disconenct A2 from the contactor coil it shouldnt get on right but I saw one contactor with A2 Removed switch on. How is this Possible

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Can I a contactor get on without connected the neutral side (A2)

06/23/2012 12:01 PM

The points may be welded together, or a combination of problems from overheating, including weakened springs, one side of points welded together, or springs so weak they don't separate far enough, or the coil could be shorted to ground....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Can I a contactor get on without connected the neutral side (A2)

06/23/2012 12:55 PM

If the contactor has your assumed isolated coil then it should not turn on. So the question is now is your assumption correct that this contactor is designed to have an isolated coil or is this a failed contactor?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Can I a contactor get on without connected the neutral side (A2)

06/23/2012 2:32 PM

If you have disconnected the final wire attached to A2 on the contactor coil, it cannot be energizing. Energizing 1/2 of a circuit is not an energized circuit.

So there are only 2 possibilities that I can think of:

  1. You are mistaken in your observation that A2 is disconnected. As SolarEagle suggested, you may have a set of welded contacts somewhere and you THINK you are opening the circuit by disconnecting it somewhere else, but in fact it is not disconnected. A simple volt meter check across A1 and A2 can eliminate that possibility.
  2. You are disconnecting the actual final wire at the A2 terminal of the coil, yet it still remains engaged. In that case, the only possibility that remains is that the coil windings have become grounded inside of the coil, and your A2 circuit is part of a grounded Neutral, so an internal path to ground makes the circuit valid for the coil power. It may be less than full voltage because of where in the coil windings it grounded, but it would/could be just enough to pull in the armature.
__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
2
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: Can I Get A Contactor Without Connecting the Neutral Side? (A2)

06/24/2012 2:48 PM

Additionally some brands of contactors have TWO A2 terminals and the coil could be getting back-fed through a circuit connected through the second A2 terminal.

__________________
jack of all trades
Register to Reply Good Answer (Score 2)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5
In reply to #4

Re: Can I Get A Contactor Without Connecting the Neutral Side? (A2)

06/25/2012 2:11 PM

Excellent point!

Siemens 3RT Series IEC contactors in many size ranges are like that for sure.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Commentator

Join Date: Aug 2010
Posts: 56
#6
In reply to #5

Re: Can I Get A Contactor Without Connecting the Neutral Side? (A2)

06/25/2012 4:14 PM

@jack of all trades.

You hit the nail on the head. Didnt notice the second A2 terminal. Silly me. Thanks again

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#7
In reply to #6

Re: Can I Get A Contactor Without Connecting the Neutral Side? (A2)

06/25/2012 6:44 PM

Ha, it's always the simplest things that cause the problems isn't it.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#8

Re: Can I Get A Contactor Without Connecting the Neutral Side? (A2)

06/25/2012 10:54 PM

May be coil is getting into body . Therefore there is return path for the coil current and the contactor holds even though A2 wire is removed.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

jack of all trades (2); JRaef (2); plckid (1); ramvinod (1); redfred (1); SolarEagle (1)

Previous in Forum: Problem in Current Transformer   Next in Forum: Every Day Stress

Advertisement