NCT

06/28/2012 7:54 AM

Question:

I was going through a single line diagram for one of the projects. It showed many transformers and HT panels.

The Main transformer rating was 220/33 kV, 50/60 MVA. The line CT ratio was 1500/1 A. The Neutral CT (NCT) was 400/1 A. The NGR (Neutral Grounding resistor) was 400A, 46.7Ω, 10 Sec.

For some other transformer, 33/6.93kV, 6.3 MVA, line CT ratio was 600/1 A. Neutral CT was 200/1 A. NGR rating was 200A, 10 Sec, 20 Ω

In the same schematic, at other place, there was a transformer 1600 kVA, 33/0.433kV. The line CT ratio was 2500/5 A. The NCT details for this transformer were 2500/5 A. There was no NGR provided.

I was able to calculate line CT ratios accurately based on the full load current on secondary side of transformer.

My questions are:

What are the criteria for selecting NGR?

How the NCT primary currents like 200A, 400A are arrived at?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Nov 2011
Posts: 171
Good Answers: 1
#1

Re: NCT

06/28/2012 8:35 AM
Register to Reply
Associate

Join Date: Sep 2008
Posts: 39
Good Answers: 1
#2
In reply to #1

Re: NCT

06/28/2012 8:39 AM

Great website. Thanks for posting..

Prashanth

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: NCT

06/28/2012 1:44 PM

For LV transformers most national codes forbid the use of NGR's.

Why would you want to restrict the earth path of a system that is supplying the end user?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#4

Re: NCT

06/29/2012 12:19 AM

NGR is provided to restrict the earth fault current. Normally in India 415 V side is effectively earthed (solidly grounded). Hence no NGR is provided in neutral circuit.

However, the secondary side of transformer 33/ 6.9 kV is non-effectively earthed (grounded through resistance) so as to limit the earth fault current. The neutral side CT is connected to restricted earth fault relay for tripping the circuit breaker in case the current exceeds the set value. Motor protection relay is also provided with earth fault protection which can be set for lower earth fault current for protecting the winding of high voltage motor against any possible damage.

Primary current of NCT is selected by the system designer based on the maximum allowable earth fault current. In case of single phase to ground fault the fault current will return to the star point of secondary winding through NGR and will be sensed by the NCT.

33kV system is generally solidly grounded. However, in specific cases it may be resistance grounded depending on the type of load connected to the 33kV bus or on certain application specific issues which can't be commented upon without going into details.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#5
In reply to #4

Re: NCT

06/29/2012 1:43 AM

Thanks for sharing this.

It's really enlightening to find out about how things are done in different places especially when explained by somebody who really seems to know their craft.

Cheers.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

debata07 (1); nobodysomebody47 (1); prashanthng (1); TonyS (1); Wal (1)

Previous in Forum: Line Reactors for Harmonics Reduction   Next in Forum: How to Find No. LED Luminaries

Advertisement