Line Reactors for Harmonics Reduction

06/27/2012 6:34 PM

Is it effective to install a line reactor in the primary side of a 220V/440V supply transformer rather than in the secondary side. I decided to install the line reactor in primary side since I have no access to the detailed of the equipment since it has no detailed electrical wiring diagram and all are sealed by supplier is a second hand CT-SCAN UNIT. We observed 200% inrush current everytime the equipment scan the patient. pls. comment.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Line Reactors for Harmonics Reduction

06/27/2012 7:49 PM

Is this really due to harmonics or could it be due to either capacitive inrush current or just plain normal operation of the CT-SCAN UNIT (as a line reactor won't really help with these problems).

Do you have a manual with electrical specifications you could refer to?

__________________
jack of all trades
Register to Reply
Associate

Join Date: Feb 2012
Posts: 50
Good Answers: 1
#5
In reply to #1

Re: Line Reactors for Harmonics Reduction

06/28/2012 9:56 AM

Sori no Manual from manufacturer. Thanks for your comments. Happy day!

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#2

Re: Line Reactors for Harmonics Reduction

06/27/2012 11:07 PM

contact the manufacturer.

__________________
pnaban
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Line Reactors for Harmonics Reduction

06/27/2012 11:09 PM

A CT scanner is just an X-Ray machine with a little motion control and a powerful imaging computer. From a power standpoint, it just ahs a big rectifier on the front end. Modern units are essentially a big SMPS, Switch Mode Power Supply. Having a reactor in front of it is good in terms of offerring some protection from line transients damaging the SMPS b ridge, and it will offer some mitigation of harmonics it creates. But that will not do anything for peak power surges. That is a function of the power that the machine uses. Not much you can do about that.

But why is that a problem for you?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Associate

Join Date: Feb 2012
Posts: 50
Good Answers: 1
#6
In reply to #3

Re: Line Reactors for Harmonics Reduction

06/28/2012 10:15 AM

Sir, this is a big problem for us since we experience frequent damage ( twice a year) in the G.E. CT-SCAN power supply cards. According to our G.E. technician this is abnormal for this type of equipment. By using a clamp ammeter the normal running current is 80 Amp. but it will suddenly peak at 180 Amp. in a split second then back to normal. This is observed everytime it will scan the patient.Presently we already installed protection relays in its source (phase loss, over/under voltage and over/under current). What I want to know where is the source of this problem from the power source or internal to the equipment?

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#9
In reply to #6

Re: Line Reactors for Harmonics Reduction

06/28/2012 3:08 PM

According to our G.E. technician this is abnormal for this type of equipment.

This really sounds like the manufacturer's problem that they need to fix, adding additional protection equipment yourself to fix something damaged or faulty inside the CT-SCAN is like trying to modify how a computer switch mode power supply works - you may be able to but chances are greater you will cause more damage and void the warranty.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#12
In reply to #6

Re: Line Reactors for Harmonics Reduction

06/29/2012 12:46 AM

These are good observations and nicely explained.

  • Does this observed behavior occur frequently/all the time
  • Is this observable over the space of an hour, minutes, seconds, days,weeks, months? Mean time between events?
  • Is there a correlation between the progress of the scan procedure and the observed spike?
  • When the current spike is detected what is the incoming line voltage doing? Dipping or spiking?

Have you physically walked the incoming line route to be absolutely sure that it is connected directly and exclusively to the utility supply? (there has to be reason why this was a requirement)

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Associate

Join Date: Feb 2012
Posts: 50
Good Answers: 1
#13
In reply to #12

Re: Line Reactors for Harmonics Reduction

06/29/2012 1:03 AM

Yes sir, i already checked the exclusiveness of the supply in fact it has its own monthly billing.The voltage line to line during the scanning process is at steady state only the line currents changes or spikes. Thanks for the very informative comments!!

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#14
In reply to #13

Re: Line Reactors for Harmonics Reduction

06/29/2012 1:54 AM

Line to line? You mean Line to neutral yes? or is this polyphase?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Associate

Join Date: Feb 2012
Posts: 50
Good Answers: 1
#15
In reply to #14

Re: Line Reactors for Harmonics Reduction

06/29/2012 3:36 AM

Yes, a three Phase system. line to line no voltage line to ground

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#16
In reply to #15

Re: Line Reactors for Harmonics Reduction

06/29/2012 3:48 AM

You need to check current on all phases and the LN (not LG) voltages on each as well.

What is your location?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#4

Re: Line Reactors for Harmonics Reduction

06/28/2012 3:32 AM

The last time I used a reactor was to limit fault current. Nothing to do with harmonics.

As soon as you introduce an iron core you are going to get inrush. Motors, transformers etc - its what happens.

You really need to do an analysis and find exactly what harmonics you have.

From memory I don't think the harmonics get from the secondary to the primary side of the Tx.

Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#7

Re: Line Reactors for Harmonics Reduction

06/28/2012 12:43 PM

Can you please describe that supply transformer circuit in a little more detail? Is this a step-up transformer or a dual coil type (dual primary for 220 or 440 volt connection)?

Are you sure your current clamp is not opening while you are taking measurements?

Do you have an MRI (magnetic resonance imager) in the area?

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Associate

Join Date: Feb 2012
Posts: 50
Good Answers: 1
#11
In reply to #7

Re: Line Reactors for Harmonics Reduction

06/29/2012 12:20 AM

Sir, this is a step-up transformer since our utlility standard voltage is 220V that is why we need to step-up the voltage to 440V since our equipment came from the U.S. We dont have any MRI in our hospital and this equipment has a dedicated power supplty direrctly from the utility as required by our equipment supplier. Aside from clamp ammeterwe already installed a power monitoring unit (PM 700).

Register to Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#8

Re: Line Reactors for Harmonics Reduction

06/28/2012 1:33 PM

A line reactor increases grid impedance, and is NOT advisable unless you know equipment power supply specifics, since it could cause serious problems if incompatible. And I wouldn't risk responsibility of ANY servicing or mods on a possibly damaged equipment that could cause EXTREME health hazards if miss-operated etc, without detailed manufacturer instructions AND clearance. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Associate

Join Date: Apr 2011
Posts: 43
#10
In reply to #8

Re: Line Reactors for Harmonics Reduction

06/29/2012 12:04 AM

if u try surge suppressor( operates in nano seconds) in secondary, it will open the circuit. the only botheration is u have to switch it on again.

Register to Reply
Power-User
Hobbies - CNC - New Member

Join Date: Feb 2010
Location: Vallejo, CA
Posts: 127
Good Answers: 8
#17

Re: Line Reactors for Harmonics Reduction

06/29/2012 10:16 AM

Disconnect the primary leads to the HV transformer. Now try for a scan. This will allow you to see if the mechanical or HV is causing the current spike. If the current still spikes, the gantry drive motor and associated circuits and equipment are doing it. You might have a place in the gantry rotation where it almost sticks, spiking current demand.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Feb 2012
Posts: 50
Good Answers: 1
#18
In reply to #17

Re: Line Reactors for Harmonics Reduction

07/01/2012 4:59 AM

Sir, what is the primary leads to the HV transformer? Can we run the scanner without them? Sori cannot get the message clearly.

Register to Reply
Power-User
Hobbies - CNC - New Member

Join Date: Feb 2010
Location: Vallejo, CA
Posts: 127
Good Answers: 8
#19
In reply to #18

Re: Line Reactors for Harmonics Reduction

07/01/2012 7:03 AM

You are not going to be getting scans, but opening the primary leads to the HV transformer takes that load out of the situation. If you still get the power surge when you operate the scanner, the problem is in the mechanicals, not the X-ray generation.

Register to Reply
Associate

Join Date: Feb 2012
Posts: 50
Good Answers: 1
#20
In reply to #19

Re: Line Reactors for Harmonics Reduction

07/02/2012 1:55 AM

Thanks, clear now. i will try.

Register to Reply
Register to Reply 20 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

drbobwoolery (2); jack of all trades (2); JRaef (1); kazengg (1); NotUrOrdinaryJoe (1); pnaban (1); siegfredo c. tabanag (7); silverfox (1); SimpleMind (1); Wal (3)

Previous in Forum: Panel Fault Level   Next in Forum: NCT

Advertisement