Calculation of KWH Reading of Energy Meter

06/29/2012 10:34 AM

hello everybody, i have a energy meter rated PT-66kv/110v,CT-200/1A,accuracy class0.5 and multiplt factor-1000 export type connected on 66kv feeder having CT Ratio 100-200-400/1A .what will happen to the kWH reading if i connected this meter to the 400/1A for the calculation of units consumed in the feeder.if i multiply it by 2000 to get the correct reading of the unit consumed.as the meter is design on the CT ratio -200/1A.please tell me about this.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Calculation of KWH Reading of Energy Meter

06/29/2012 11:48 PM

Could I ask why you would want to do this?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Active Contributor

Join Date: Jun 2012
Posts: 11
#2
In reply to #1

Re: Calculation of KWH Reading of Energy Meter

06/30/2012 12:35 AM

i want this because i connect the energy meter in the grid station on the 66kv out going feeder on 400/1A

Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#3
In reply to #2

Re: Calculation of KWH Reading of Energy Meter

07/01/2012 11:16 AM

Simple formula you can apply to calculate the Multiplication factor of meter system

Multiplication factor for KWH = CT ratio of line * PT ratio of line

___________________________ * scale factor of meter

meter CTR * meter PTR

__________________
Exploring the Science of Electricity
Register to Reply
Active Contributor

Join Date: Jun 2012
Posts: 11
#4
In reply to #3

Re: Calculation of KWH Reading of Energy Meter

07/02/2012 12:16 AM

please illustrate this formula with the help of example so that i can understand this properly, i will be very grateful to you for helping this.

with regards

sehdev singh

Register to Reply