Calculating Elect. Consumption for 3 Phase Rectifier/Transformer

07/04/2012 6:55 AM

Dear Sir,

I have a 3 phase rectifier/transformer that I use for electro plating.

Consumption is as follows:

Phase 1 = 20 amps

Phase 2 = 19 amps

Phase 3 = 21 amps

Voltage Line to Line = 420Volts AC

Voltage Line to neutral = 230 Volts AC

Hz= 50

Power factor = 0.80

Please advise how many watts the rectifier is using.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster #1
#1

Re: Calculating elect. consumption for 3 phase rectifier/transformer

07/04/2012 7:08 AM

The figure is the power going into the rectifier minus the power going out of the rectifier. Unless I'm very much mistaken, that information is missing from the figures you have provided.

Register to Reply
Member

Join Date: Jul 2012
Posts: 8
#2
In reply to #1

Re: Calculating elect. consumption for 3 phase rectifier/transformer

07/04/2012 7:12 AM

This is the AC power going into the rectifier. On the output of rectifier I am getting dc volts but that is another discussion.

Register to Reply
Anonymous Poster #1
#4
In reply to #2

Re: Calculating elect. consumption for 3 phase rectifier/transformer

07/04/2012 7:57 AM

You still can't do it.

Register to Reply
Member

Join Date: Jul 2012
Posts: 8
#3
In reply to #1

Re: Calculating elect. consumption for 3 phase rectifier/transformer

07/04/2012 7:36 AM

Or you can think of this as an electric motor instead of a rectifier. I just need to know how to calculate the KW being consumed.

Thanks.

Register to Reply
Anonymous Poster #1
#5
In reply to #3

Re: Calculating elect. consumption for 3 phase rectifier/transformer

07/04/2012 8:06 AM

You still can't calculate the watts being dissipated by the rectifier because you don't have enough data to measure what's coming out. You only know what's going in.

Register to Reply
2
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#6

Re: Calculating elect. consumption for 3 phase rectifier/transformer

07/04/2012 8:25 AM

You may calculate the watts consumed by using the formula:

W=V X I X PF for each of the 3 phases and add up to get the total power as below:

For phase-1 :230 X 20 X 0.8 =3680

For phase-2 :230 X 19 X 0.8 =3496

For phase-3 :230 X 21 X 0.8 =3864

-----------

Total watts =11040

-----------

Alternatively, use the formula for 3 phase power : \/3 X V-Line-Line X I X PF

=1.732 X 400 X 20 X 0.8

Total watts =11084.8 (almost same as above)

Please note that as per calculation V Line-Line =\/3 X V Line-Neutral

=1.732 X 230 =398.36

(say 400 not 420 Volts) and the balanced phase current can be assumed as 20 Amps.

__________________
Learning is a never-ending process.
Register to Reply Good Answer (Score 2)
Anonymous Poster #1
#7
In reply to #6

Re: Calculating elect. consumption for 3 phase rectifier/transformer

07/04/2012 9:59 AM

Please advise how many watts the rectifier is using

Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8
In reply to #7

Re: Calculating elect. consumption for 3 phase rectifier/transformer

07/04/2012 10:27 AM

He just did. Please learn abouit electricity before posting.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Off Topic
Member

Join Date: Jul 2012
Posts: 8
#12
In reply to #6

Re: Calculating elect. consumption for 3 phase rectifier/transformer

07/04/2012 6:05 PM

Thank you Spradhan. You understood my question correctly. I was only looking for KW consumption of my rectifier. Your answer seems correct to what I was thinking. For others "I am not interested in the efficiency of the rectifier so its got nothing to do with the power coming out in DC. Just plain and simple I was looking for the consumption of the rectifier." Thanks again Spradhan.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#13
In reply to #12

Re: Calculating elect. consumption for 3 phase rectifier/transformer

07/04/2012 7:45 PM

Then you should have asked about the power consumption of the electroplating system...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#9

Re: Calculating elect. consumption for 3 phase rectifier/transformer

07/04/2012 10:41 AM

As others have stated above, you can't with the information you have provided. What's missing is the power consumed on the load (plating) side of the rectifier/transformer combination. It seems that you want to make a distinction between AC power and DC power, don't, because there isn't any; power is the instantaneous amount of work being done.

Simply take the DC Amps X DC Volts= Watts into the plating solution and subtract it from the Watts going into the transformer/rectifier combination. This will be the Watts lost in the conversion from AC to DC.

If you want to know the loss in only the transformer and rectifier separately you will have to measure the voltage drop across each and apply the appropriate formula, but this is definitely not something that you should do at these voltage and current levels.

One more thing, is the 0.8 PF read off a meter or is it from the equipment rating? If it is from the nameplate then there may be an error in the AC calculation due to the difference between ratings and actual usage conditions.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#10

Re: Calculating Elect. Consumption for 3 Phase Rectifier/Transformer

07/04/2012 12:08 PM

Assuming you have 20 x 3 amps going in you should have around 60 amps DC coming out so figuring the average rectifier diode has a .7 volt drop and that two are conducting at anyone time the rectifiers estimated power consumption would be around (60 x 1.4 =) 84 watts give or take.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#11

Re: Calculating Elect. Consumption for 3 Phase Rectifier/Transformer

07/04/2012 1:26 PM

If I'm correct, you are looking for the current loss through rectification of your 3Ø AC current to DC current....This will vary according to rectifier type and operating conditions....If you just need an approximate number you could quantify the loss at between 10% and 20%....If you need an accurate figure than you must use the method described above, by subtracting output of current from input...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Member

Join Date: Jul 2012
Posts: 8
#14
In reply to #11

Re: Calculating Elect. Consumption for 3 Phase Rectifier/Transformer

07/05/2012 4:16 AM

Thank you Spradhan. You understood my question correctly. I was only looking for KW consumption of my rectifier. Your answer seems correct to what I was thinking. For others "I am not interested in the efficiency of the rectifier so its got nothing to do with the power coming out in DC. Just plain and simple I was looking for the consumption of the rectifier." Thanks again Spradhan.

Register to Reply Score 1 for Good Answer
Member

Join Date: Jul 2012
Posts: 8
#15
In reply to #14

Re: Calculating Elect. Consumption for 3 Phase Rectifier/Transformer

07/05/2012 4:25 AM

Now the story gets a little more interesting. Now that the load is calculated via

\/3 X V-Line-Line X I X PF

=1.732 X 400 X 20 X 0.8

Total watts =11084.8

The energy meter supplied by the power company is giving a reading of 5KW per hour instead of 11KW. How is that possible?

The amps going into the rectifier were calculated using an accurate clamp meter and the voltage was also checked via an accurate multimeter.

The rectifier is a full wave diode type rectifier if that helps. Appreciate your comments on this one.

Register to Reply
Anonymous Poster #2
#16
In reply to #15

Re: Calculating Elect. Consumption for 3 Phase Rectifier/Transformer

07/05/2012 5:22 AM

Shhh--we won't tell if you don't.

Register to Reply
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#17
In reply to #15

Re: Calculating Elect. Consumption for 3 Phase Rectifier/Transformer

07/05/2012 7:10 AM

The values of Current and voltage given in your original post are instantaneous values at the moment of measurement by clamp meter.Hence the calculated power is also instantaneous power.

To find the average power consumption,you have to take the energy meter readings at regular intervals (say 24 hours/30 days etc.) and determine the difference between two consecutive readings.Dividing this value by the No. of hours in the said interval will give the average power consumption.

Hope this clarifies the matter.

__________________
Learning is a never-ending process.
Register to Reply
Power-User
Canada - Member - New Member

Join Date: Feb 2010
Location: The Great White North
Posts: 185
Good Answers: 13
#18
In reply to #15

Re: Calculating Elect. Consumption for 3 Phase Rectifier/Transformer

07/05/2012 1:01 PM

My guess is that you have a constant voltage rectifier. This type of rectifier will vary the current produced depending on the applied load in the plating tank while maintaining the same output voltage. So at one moment when the load is in the tank it may be using 11 Kw but when the load is removed from the plating solution the current used is reduced dramatically. The 5Kw usage from your supplier is an average usage.

Elroy

__________________
Knowledge makes what was impossible, seem easy.
Register to Reply
Member

Join Date: Jul 2012
Posts: 8
#19
In reply to #18

Re: Calculating Elect. Consumption for 3 Phase Rectifier/Transformer

07/05/2012 2:06 PM

Actually Elroy the irony is that the plating load is constant. We electrowin copper from copper sulphate solution and the plating area is the same. I guess the right question is that if you have an average clamp meter reading of 20 amps per phase and the voltage is 400 VAC and according to the formula you get 11kw consumption. But can real energy consumed be less by as much as 50% than the amps that are being shown on the clamp meter?

Register to Reply
Power-User
Canada - Member - New Member

Join Date: Feb 2010
Location: The Great White North
Posts: 185
Good Answers: 13
#20
In reply to #19

Re: Calculating Elect. Consumption for 3 Phase Rectifier/Transformer

07/05/2012 8:38 PM

But can real energy consumed be less by as much as 50% than the amps that are being shown on the clamp meter?

I don't think so.

There are three possibilities that I can think of and I'll place them in order of likelihood.

1 You have a faulty amp-meter.

2 The amp-meter is of poor quality and is affected by the poor power factor and harmonics produced by your rectifier. ( I have done hundreds of amp-meter checks on rectifiers and have never had this issue although our power factor is kept at .98 to 1 Try a different meter.)

Remember the rectifier SCRs may only be using part of the sign wave. Your amp-meter may not know the difference but your service providers meter might.

3 Your electrical providers meter is malfunctioning and you are getting a sweet deal. ( Not likely)

__________________
Knowledge makes what was impossible, seem easy.
Register to Reply Score 1 for Good Answer
Member

Join Date: Jul 2012
Posts: 8
#21
In reply to #20

Re: Calculating Elect. Consumption for 3 Phase Rectifier/Transformer

07/06/2012 4:08 AM

Elroy. I will check the amp meter and also verify with another energy meter and revert to you.

Thanks bro.

Register to Reply
Register to Reply 21 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (5); Elroy (2); kasco (7); RAMConsult (1); SolarEagle (2); spradhan (2); tcmtech (1); Tornado (1)

Previous in Forum: LT Panel Clearance   Next in Forum: Transformer Winding Resistance

Advertisement