Single Phase Cycloconverter With Voltage Reduction

07/04/2012 10:16 AM

We have to design an UPS with Input is AC 230V, 1phase, 50 Hz. Output as 110V AC, 60 Hz. The output is catering to a load of 10 kVA. (18 Amp per workstation x 5 such workstations@ 110V)

how can we equate the Input power with output power, even when there is change of frequency between output and input voltages.

OR

Is our sizing of 10 kVA of UPS is adequate?

What shall be the size of Incoming breaker of UPS?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: single phase cycloconverter with voltage reduction

07/04/2012 10:27 AM

Hire an electrical design engineer to do the work. (Or maybe a smart high school student)

You must be in management.

Register to Reply
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: single phase cycloconverter with voltage reduction

07/04/2012 10:34 AM

A1: The output power divided by the input power is the efficiency. There will be a loss of power to effect the voltage and frequency conversions.

A2a: With no diversity on the output, the UPS is going to be on the upper limit of its capabilities.

A2b: The incoming breaker needs to be sized to handle a load larger than the maximum rating of the UPS, otherwise the breaker will trip before the UPS runs out of headroom, which will be a nuisance. Further, the incoming feed needs to cater for the situation where the UPS is re-charging as well as supplying the load, which makes the incoming feed somewhat bigger than 10kVA. Sizing of the breaker and the incoming cabling takes place according to the national wiring regulations in place in the country of installation; in the UK it's back to good old British Standard 7671 again.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Register to Reply 2 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

Previous in Forum: Transformer Winding Resistance   Next in Forum: Question: Electronic Flow Adjuster?

Advertisement