I am currently working on getting a 2.5 MW Genset installed and integrated to the existing control system. During the startup, I have the genset technician and the systems integrator working side by side. For some reason, once the breaker closes, we are seeing negative VARS. The CATS tech points the finger to the integrator and the integrator points it back to the tech.
I need clarification as to what might be the problem. Below is an excerpt from the integrator's report stating what we have seen.
Initially the DSLC does volt matching with the bus and controls the regulator by sending a 0-10VDC signal. After the breaker is closed inputs 48 and 49 on the DSLC are energized and the DSLC goes into power factor control. It again sends a 0-10VDC signal to the regulator to maintain the power factor setting that I have programmed into the DSLC (currently set at .92 lagging). From what I can see on RIMCO regulator program it appears that the DSLC is trying to control the power factor (evident by the 0-10VDC signal increasing from 1.42VDC to over 3VDC) yet the generator seems to slowly walk away from the bus voltage until the protection relays trips out the breaker on negative VARS. VARS is what you get when your power factor suffers. Again I'm not 100% convinced that its not my problem, but until someone proves otherwise I can't think of anything that would cause this issue from my end.
Desperately needs someone to point us in the right direction.