VFD for Chilled Water Pumps and Condenser Water Pumps

07/06/2012 2:32 AM

Hello Sir,

The company is going into energy conservation program, since it is not possible to use VFD on piston type refrigeration compressor can we use VFD for chilled water pumps and condenser water pumps for the chiller since this is centrifugal type of pumps.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#1

Re: VFD for chilled water pumps and condenser water pumps

07/06/2012 3:07 AM

If they really want to save energy and money start by firing people in the upper office levels until they are down to just enough people that everyone is actually working as long and hard of hours as the people at the bottom are!

Instead of spending millions to save thousands you could end up saving millions and actually become a more efficient company too which would really be worth value in the end.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: VFD for chilled water pumps and condenser water pumps

07/06/2012 3:13 AM

Before investing in VFDs, try other things.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: VFD for chilled water pumps and condenser water pumps

07/06/2012 4:03 AM

Why not just try turning off the lights when you leave the room first.

Register to Reply
Commentator

Join Date: Sep 2009
Location: INDIA
Posts: 92
#4

Re: VFD for chilled water pumps and condenser water pumps

07/06/2012 4:27 AM

Explain why it is not possible for piston type compressor to use VFD?

It is possible.Also you can use it for chiller sas wel

Register to Reply
Associate

Join Date: Apr 2012
Posts: 42
Good Answers: 1
#5
In reply to #4

Re: VFD for chilled water pumps and condenser water pumps

07/06/2012 11:03 PM

All things are possible - reciprocating loads can cause issues w/ VFD's that typically are not seen w/ across the line MSP's - because the VFD can / does react faster to changing load, etc. on / at the motor. Sometimes just oversizing the VFD is enough.

Centrifugal pumps are less of a problem, forget the word for the principle, simply put the pump curve changes as a function of speed (NPSHR, TDH, Q, HP). Generally in mostly inconvenient ways, but can and is done.

Register to Reply
Associate

Join Date: Apr 2012
Posts: 42
Good Answers: 1
#9
In reply to #5

Re: VFD for chilled water pumps and condenser water pumps

07/07/2012 1:59 PM

And think a little about changing speed on lubricated equipment, e.g. compressors.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6

Re: VFD for Chilled Water Pumps and Condenser Water Pumps

07/06/2012 11:30 PM

Yes it is. I'm not sure what the ROI will be.

Get the bean counters upstairs to work that out.

You can do lots of things but it doesn't always yield a real saving.

Of course if you just want to reduce energy consumption because of either a supply/resource limitation or your company needs a green halo and not doing it to save money then knock yourself out.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#7

Re: VFD for Chilled Water Pumps and Condenser Water Pumps

07/07/2012 12:13 AM

What is the capacity of these pumps and its operating pattern. How big is the size of the chiller. If you consider VFD for pumps then why nit at AHUs?. By observing the operating parameters and carrying gout regular maintenance is another way to save energy in central a.c plants.

Register to Reply
Guru
Popular Science - Evolution - New Member

Join Date: Jul 2006
Location: India-Chennai.
Posts: 722
Good Answers: 30
#8

Re: VFD for Chilled Water Pumps and Condenser Water Pumps

07/07/2012 10:25 AM

" it is not possible to use VFD on piston type refrigeration compressor "

Has your recip compressor unloading/partially loading facility?

__________________
A picture worth thousand words: needless to say if it is animated.
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#10

Re: VFD for Chilled Water Pumps and Condenser Water Pumps

07/08/2012 5:59 PM

jhunair,

In one word, yes. Centrifugal pumps follow what are often called the "fan laws", which relate changes in speed to changes in power and flow. Most of the time, pumps are originally designed and installed with somewhat excess power compared to the actual load. If you have a good design for control, a VFD will allow the pump speed (and volume) to match the load, particularly as the load changes because of changes in refrigeration loads. This will result in considerable savings when the loads are light. A phrase often used is "the devil is in the details". Probably you have a similar form of statement in your country.

--JMM

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#11

Re: VFD for Chilled Water Pumps and Condenser Water Pumps

07/09/2012 4:07 AM

The reciprocating pumps are not as easy to control as say a vane pump but you can still use a VSD. Turndown will only be partial though compared to a vane pump.

Register to Reply
Active Contributor

Join Date: Aug 2009
Posts: 21
#12

Re: VFD for Chilled Water Pumps and Condenser Water Pumps

07/09/2012 12:47 PM

Condenser water pumps connect to cooling towers that are fitted with nozzles which have a fairly narrow max/min flow requirement. Inadequate flow will cause scale build up. Also, cooling tower fan motors connected to centrifugal fans could overload with reduced water flow. VFD's on condenser water aren't such a good idea.

They are great for cooling tower fan motors. OK for chilled water as well as long as flow doesn't become laminar at the heat exchanger.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Feb 2011
Posts: 40
#13

Re: VFD for Chilled Water Pumps and Condenser Water Pumps

07/10/2012 4:35 PM

Hello Sirs,

Thank you for all the inputs I thought adding VFD can have effect on energy savings you have to consider many factors.

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#14

Re: VFD for Chilled Water Pumps and Condenser Water Pumps

07/13/2012 7:39 AM

First of all u have to see how long pumps are going to run at Different load conditions and then what variations.If it is going to be a operation for short time initially and then run on full load it may be sensible to use a smaller pump and then switch over.Whole process needs to be analysed before a decision and investment is made.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Register to Reply 14 comments

"Almost" Good Answers: