Sizing a Generator

07/06/2012 5:58 AM

What will be the standard size of a generator for a 100 kva single phase step-down transformer supply. Is a 125KVA gen-set enough size to this kind of load in a hospital building? Pls. comment.

Register to Reply
Pathfinder Tags: Generator Sizing
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jun 2007
Location: ether
Posts: 371
Good Answers: 1
#1

Re: Sizing a Generator

07/06/2012 7:05 AM

put it this way... how much does cost a 125 KVA gen, and how much does it cost a 200KVA gen... if you had to pay 1k more for the second I would recommend having the second. and then perhaps you could feed 2 steppers

__________________
“For no man can forbid the spark nor tell whence it may come.” ? Francis Bacon
Register to Reply
Associate

Join Date: Feb 2012
Posts: 50
Good Answers: 1
#5
In reply to #1

Re: Sizing a Generator

07/06/2012 8:29 PM

Thank you sir, You are correct the price diffrence is minimal as we go higher in KVA ratings for Gen-set. Is the fuel consumption of a bigger gen-set varied much? Anyway we only load the gen-set maybe at most 5-6 times a year. we warm-uped the engine once a week for 10 minutes!!

Register to Reply
Commentator

Join Date: Sep 2009
Location: INDIA
Posts: 92
#2

Re: Sizing a Generator

07/06/2012 7:09 AM

IF YOU CONSIDER 25% MARGIN THEN IT IS CORRECT .YOU SHOULD GO FOR SINGLE PHASE DIESEL GENRATOR.

BUT WHAT IS THE VOLTAGE OF TRANSFORMER PRI/SEC.?

Register to Reply Score 2 for Off Topic
Associate

Join Date: Feb 2012
Posts: 50
Good Answers: 1
#4
In reply to #2

Re: Sizing a Generator

07/06/2012 8:15 PM

Sir, in the Philippines our utilities supply 13.2KV in Primary / 220V secondary. Thank you for your advise. Godbless and more power to you.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6
In reply to #2

Re: Sizing a Generator

07/06/2012 11:53 PM

125kVA single phase?

Not likely.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Associate

Join Date: Feb 2012
Posts: 50
Good Answers: 1
#7
In reply to #6

Re: Sizing a Generator

07/07/2012 6:49 AM

Yes Sir, this is a single-phase 220V 125KVA transformer, the supplier need to reconnect the generator windings in order to deliver a single phasesupply at 220V, wherein it is clear that our required max. full load current is attained at full load.

Register to Reply
Power-User

Join Date: Jun 2007
Location: ether
Posts: 371
Good Answers: 1
#10
In reply to #2

Re: Sizing a Generator

07/10/2012 9:51 AM

Hello luv123 ;) yes, I did forgett to mention the margins! cheer´s again!

__________________
“For no man can forbid the spark nor tell whence it may come.” ? Francis Bacon
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Sizing a Generator

07/06/2012 12:58 PM
Register to Reply Off Topic (Score 5)
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#8

Re: Sizing a Generator

07/08/2012 11:04 AM

Can u tell us why are you using a single phase 100kva? what is the type of Load?

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Associate

Join Date: Feb 2012
Posts: 50
Good Answers: 1
#9
In reply to #8

Re: Sizing a Generator

07/09/2012 7:27 AM

We are using this generator for a single-phase 220V school building load with night school sked till 10 a.m.

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#11
In reply to #9

Re: Sizing a Generator

07/11/2012 3:04 AM

To select a suitable generator load details is essential...

__________________
To avoid crticism do nothing,say nothing,be nothing