Step Voltage?

07/06/2012 7:18 PM

In light of the electrocutions that took place over the July 4th, I am wondering if it would be possible to verify electricity in the water. I'm proposing using two lengths of PVC pipe fitted with a copper sleeve. Figure an 8ft piece of PVC with a 3 foot length of copper tube, fitted with leads to the surface. Lower these in the water with say 5 ft of separation and then measure the leads for an AC potential between the two rods. Obviously, multiple tests would have to be made to verify a safe area, and once tested no additional items can be energized. Might be possibly to use multiple probes with an audio device. My concern of course is that it may give a false sense of safety, when in fact a hazard exists.

With the advent of powerful inverters and portable generators, (none of which are approved for marine use) I think incidents of this nature are only going to increase.

Register to Reply
Pathfinder Tags: marine safety
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United States - Member - USA! Hobbies - Musician - Sound Man Engineering Fields - Mechanical Engineering - More than a Hobby Technical Fields - Technical Writing - New Member

Join Date: Oct 2008
Location: City of Roses.
Posts: 2056
Good Answers: 101
#1

Re: Step Voltage?

07/06/2012 7:56 PM

I think DC would work... AC I have a hard time thinking it would work.

__________________
Don't believe everything you read on the Internet!
Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Step Voltage?

07/06/2012 10:42 PM

It's relatively easy to determine if there is an electric field in water, what's difficult is where to put the sensor. If the field was between two point sources and the sensor was not near them then no warning would be given.

In most of the well maintained marinas I've been in the dock-side power pedestals were properly grounded and equipped with GFCIs. The ship-side power systems were all solidly grounded and bonded to a common point which connects to the pedestal through a 4-wire Twist-lock connector thereby ensuring that no potential difference exists between the metal of boat and the power supply. Even if the boat is running on its own generator it is still bonded to the shore supply so there is no potential difference between the boat and the dock. On the other hand I have docked where I was really concerned about plugging into dock power after observing ordinary extension cords, corroded grounds, open junction boxes or dozens of other obvious safety hazards.

There are plenty of inverters, converters and generators that are designed and qualified for marine pleasure craft use. I wouldn't blame properly designed, installed, maintained, and utilized electrical equipment. More than likely it was electrical wiring that was installed by unqualified personnel and/or was not properly maintained that contributed to these unfortunate events.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#12
In reply to #2

Re: Step Voltage?

07/08/2012 7:53 PM

The one fly in the ointment in the above scenario happens when someone uses a UL approved appliance having the green safety wire and the white neutral connected. Although everything else is compliant to code this one connection while required on land is not approved on a boat especially a metal hulled boat.

Return current in the white wire splits at the point where the plug in appliance has the green and white wire joined as required by UL.

The part of the return current which follows the green wire is not sufficient to trip a breaker.

Furthermore if the metal hulled vessel is new and compliant with best practices it may have an isolation transformer. This means a GFCI on the dock will never trip either. However stray current in any vessel will circulate in the green safety wiring and the code compliant 'bonding' wiring that connects thru hulls in the vessel. A step potential can easily be set up - especially in fresh water.

__________________
Elnav
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#3

Re: Step Voltage?

07/07/2012 11:54 PM

Which electrocutions are we talking about? It didn't make the news here.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Power-User

Join Date: Jun 2011
Location: Caerdydd, Cymru
Posts: 171
Good Answers: 12
#4
In reply to #3

Re: Step Voltage?

07/08/2012 2:16 AM

http://www.bbc.co.uk/news/world-us-canada-18725859

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6
In reply to #4

Re: Step Voltage?

07/08/2012 11:15 AM

Thanks

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
Popular Science - Weaponology - New Member Fans of Old Computers - PDP 11 - New Member Technical Fields - Architecture - New Member Hobbies - HAM Radio - New Member

Join Date: Oct 2009
Location: Maine, USA
Posts: 2168
Good Answers: 71
#5

Re: Step Voltage?

07/08/2012 7:36 AM

So if the wiring on a mobile platform (house boat) is defective, how will a stationary device be able to detect a problem that can be moved at random??

__________________
Tom - "Hoping my ship will come in before the dock rots!"
Register to Reply
Guru
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2011
Location: 18N 65W o
Posts: 1003
Good Answers: 28
#7
In reply to #5

Re: Step Voltage?

07/08/2012 12:53 PM

That sir is one of the question(s) I posed. What are your thoughts?

And I don't know that it was a houseboat, in fact one took place in a marina. The articles didn't state whether or not a vessel electrical system was involved, only that an investigation is ensuing.

As I stated, with the advent of high power inverters and generators that are not marine rated, all things are possible. Marine rated devices are available, but are 3 times the cost. It seems that people feel the marine rating (USCG approved) is nothing more than a license to raise prices.

Another poster stated something about DC. While there are documented cases of electrocution with 28 VDC, DC is a self correcting. If the DC leakage is not corrected, the offending vessel will sink.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#13
In reply to #7

Re: Step Voltage?

07/08/2012 11:33 PM

If it is an aluminium boat tied to a steel boat with a steel rope it will sink without any additional DC hurry up.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply Off Topic (Score 5)
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#8

Re: Step Voltage?

07/08/2012 6:57 PM

I work in the marine electrical field and this kind of problem is not as easy to fix as some posters imply. It can happen even when proper marine grade and type approved equipment is used. Even the experts cannot agree on one solution.

It is regrettable that these fatalities occurred and as always people are quick to start a witch hunt to nail someone with blame. I intend to track this story because I work in the field. I suspect the accident investigation will uncover a few surprises.

__________________
Elnav
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#9

Re: Step Voltage?

07/08/2012 6:59 PM

Dock-side equipment without a GFCI appears to have been the problem at at least one site:

http://articles.kspr.com/2012-07-05/electrocution-death_32555705

"...Officials say there was no ground fault interrupter to monitor the current and trip the electricity if there was a problem. They say the electricity could have come from several sources, including a boat lift or a pump used to power a water slide...

Sad that not using a $15 device caused this tragedy, hopefully others will learn from it.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#10
In reply to #9

Re: Step Voltage?

07/08/2012 7:21 PM

Use of a 5ma GFCI may not have been the solution. The report I linked to said the boys were swimming between two house boats and would be rescuers felt a strong paralyzing tingle until power on the boat was shut off.

One possibility as a cause would be the plugging in of an approved household device in the houseboat system.

This reaches into an area where even the experts sometimes disagree as to the solution.

I once encountered a shock hazard in a government installation only two years old. The work was done by qualified contractors using approved work practices and mostly certified equipment. A GFCI did nothing to prevent the problem. The problem location was located upstream of the GFCI.

__________________
Elnav
Register to Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#11
In reply to #9

Re: Step Voltage?

07/08/2012 7:39 PM

Sometimes the wiring itself leaks current despite being fairly new. Outdoor equipment normally uses SJOW grade of wiring. This is rated for outdoor use and as such is UL approved. unfortunately many people mistakenly think 'outdoor' means water proof. It is and it ain't. For submerged continuous use you need to use 'submerged cable' not outdoor rated. I have tested 18 month old UL approved outdoor grade wire and found it failed the megger test. Plastic wiring insulation will permit electrons to migrate through the insulation. As the wire ages some of the plasticizer molecules evaporates leaving a void in the plastic structure. Water molecules migrates through these voids and eventually leads to leakage current.

If you submerge SJOW wire full time it will fail in a couple of years but not enough to trip a circuit breaker.

We all know what happens when nuisance trips keep occuring. Somebody finally bypasses it when they cannot find an obvious cause. Not finding the cause and no cause being present is not the same thing.

Unfortunately land based electricians do not get in-depth training as marine electricians so they may not be fully conversant with the finer details.

__________________
Elnav
Register to Reply
Register to Reply 13 comments