ELCB Tripping?

07/07/2012 2:10 AM

Hello Guys..!

In one of my Installation all the Lighting Circuits are connected to 30mA ELCB , 63A ( Max connected Load is 42Amps) .

Observation:

When we Switch On all the Lights apart from LED Cove Strip ( 5W/Mtr , Driver 12VDC SMPS) it is working fine and when we switch on the Strip for First Time it is working Fine, The Tripping Starts only when we Switch Off and On the LED Strip for 2 nd or 3 rd time.

What could be the Problem?

We removed the Strips from the Cove and checked all the connection , There is not Loose Connection or SC. FYI: I normally Stick the Flexible Strips on the Aluminium Channel ( Reason :1 to get more Heat Dissipation , 2 to Form a Straight Line).

I dont see any contact with the Strip or with the False Ceiling Channel.

Can I increase the ELCB to 100 or 300 mA?

What to do?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Associate

Join Date: Jul 2012
Posts: 39
#1

Re: ELCB Tripping?

07/07/2012 5:03 AM

I am going to take a quick guess here and suggest the problem is your using SMPS instead of LED Driver concurrently with 30mA sensitivity for your ELCB.

The reason is SMPS Drivers will regulate the voltage but will not supply a constant current, perhaps it's why the tripping only takes place after toggling the switch rather than immediately after staring your circuit.

I would suggest trying 100mA sensitivity first and see if that takes care of it, but unless your circuit is non-experimental. I would go with changing from SMPS to LED-Driver.

Register to Reply
Member

Join Date: Jul 2012
Location: COIMBATORE,TAMIL NADU , SOUTH INDIA
Posts: 5
#2
In reply to #1

Re: ELCB Tripping?

07/07/2012 6:07 AM

Thanks for the Information. Let me try with 100mA ELCB.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2010
Location: 1° North Singapore
Posts: 568
Good Answers: 17
#3
In reply to #1

Re: ELCB Tripping?

07/07/2012 9:10 AM

All Strip Led lights that i have seen are designed to have constant voltage drive, therefore normal smps is ok. Using constant current LED drive would be wrong. From your data, the loading is already quite high and the tripping occur when you turn on. This looks very much like start up surge current. Some poorly designed smps has very high start up surge current. So 42 A plus a little more surge current will cause tripping. Solution, use another mcb to reduce current, or insert a series anti surge current realtor to the input to smps.

__________________
Sharing knowledge is one thing that defies basic arithmetic logic --- the more you share, the more you get!
Register to Reply
Associate

Join Date: Jul 2012
Posts: 39
#4
In reply to #3

Re: ELCB Tripping?

07/07/2012 12:33 PM

LEDs are current driven devices, SMPS will be fine but will require adding a resistor to regulate the current, otherwise your LED's will not function properly with respect to time as temp. rises.

Changing the ELCB from 63A to the next step (80A) is unacceptable.

If you decide the inrush of your PS is the issue, then you must separate the LED from the other lighting loads. If your MCB is 200% your rated load you will risk failed tripping on your lighting loads when needed. Typically the Lighting circuits are grounded by the lights frame which takes care of currents like 35mA, if your ELCB has 100mA sensitivity, this will interrupt any reasonable leaks, otherwise, 35mA is likely to be the problem for the tripping.

If your lighting loads are fluorescent, then I can tell you I am certain your problem is the ELCB sensitivity, because fluorescent light produces harmonics that will cause your interrupting devices to trip at 35mA sensitivity.

Register to Reply
Associate

Join Date: Feb 2009
Location: India
Posts: 45
#5

Re: ELCB Tripping?

07/07/2012 10:44 PM

Please, Check your wires for current carrying capacity. If any wire gets heated up, replace it.

__________________
Ram
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6

Re: ELCB Tripping?

07/07/2012 11:11 PM

Is it tripping on over current or earth leakage?

You have to know what is actually happening before trying to remedy.

All connected to one 63A breaker? No branch circuits? What is the conductor size?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Jul 2010
Location: North West Province, South Africa
Posts: 67
Good Answers: 18
#10
In reply to #6

Re: ELCB Tripping?

07/08/2012 10:28 AM

Hi Wal,

Voted you a GA based on asking the obvious - is this an earth leakage problem or an over current problem?

Regarding the use of earth leakage devices - these are installed primarily to protect the user against dangerous leakage voltages occurring on an electrical circuit and the normal leakage current value of the breaker installed in domestic applications would be 30mA.

Raising the earth leakage trip value to 100mA or more, basically defeats the purpose of the earth leakage breaker in the domestic application and will allow dangerous leakage to occur before interrupting the supply. This won't remove the problem but may remove the user!

I am aware that higher value earth leakage devices are used in industrial applications.

Earth leakage breakers are available in two formats - those with over-current protection and those without. In SA the breaker handle colour normally indicates which version you have with a white handle (lever) indicating over-current protection and a green handle indicating an isolator with no over-current protection. Both versions would be rated to trip if the earth leakage exceeds the rating of 30mA.

My suggestion to Senthilnair is examine the earth leakage breaker to determine which version is installed (check the label) and, secondly, monitor the current being drawn by the circuits when the trip occurs. As the other posters have indicated, rapid switching of a load that has a high inrush current will lead to a sustained inrush current which will result in an overload trip. Lastly, an insulation test would indicate if there is, in fact, and insulation breakdown (or other fault) which would lead to an earth leakage trip.

If you have an earth leakage clamp meter (a clamp/tong tester with a low range allowing measurement of mA) tester you could connect this around the cables on the load side of the earth leakage breaker and be able to 'see' the unbalance in the circuit i.e. what goes out on the live should be equal (within the 30mA allowed by the breaker) otherwise you have a leakage problem.

Hope this is of assistance to you!

Regards, Keith

__________________
A little knowledge that acts is worth infinitely more than much knowledge which is idle! Khalil Gibran
Register to Reply
Member

Join Date: Jul 2012
Location: COIMBATORE,TAMIL NADU , SOUTH INDIA
Posts: 5
#12
In reply to #10

Re: ELCB Tripping?

07/09/2012 12:47 AM

Hi Keith,

Thanks for the Info,I really appreciate your effort.

Ill ask my Team to balance the Circuits in full Load.

Keep you posted.

Regs,

Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: May 2011
Posts: 23
Good Answers: 2
#7

Re: ELCB Tripping?

07/08/2012 2:09 AM

Hi Senthilinair,

Curiosity: Could you be using a Lutron Lighting Control panel with remote controllers and with a internal LV dimmer circuit for your LED?

I had one installation that sounds almost word for word your problems and it was related to the dimming circuitry for the LED portion of the panel-- I had multiple dimmable circuits under control with low voltage and 220 in the panel on 32A circuit--- Neither Lutron nor I could make it work. I did a work around by putting the LV dimming circuit on its own mains circuit breaker.

Expat 07

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8

Re: ELCB Tripping?

07/08/2012 2:43 AM

The problem seems to be due to leakage currents from the trigger electronic circuits of the LED Lighting. Pl. try a hi-sensitivity ELCB that are specifically made for such applications, in which case, you can still stick to 30mA sensitivity of the ELCB.

Register to Reply
Member

Join Date: Dec 2011
Posts: 7
#9

Re: ELCB Tripping?

07/08/2012 9:58 AM

nothing is reason for your tripping except below reason: It is due to leakage betweeen strip and alu body used as heat sink. Use a Mica sheet between Alu body and strip An ELCB will not trip on even short circuited.

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#11

Re: ELCB Tripping?

07/08/2012 3:30 PM

The reason it tripped, Boss, is because there is an imbalance between live and neutral in excess of 30mA. Something connected onto the circuit is faulty, and you'd do best to find it and replace it before it replaces someone who becomes inadvertently connected to it.

__________________
Good moaning!
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#13

Re: ELCB Tripping?

07/09/2012 4:04 AM

Are we talking an ELCB are an RCD. If its an old voltage operated ELCB that operates when it senses volts on the earth even a neighbours house can cause you a problem.

Assume its an RCD where there has to be a balance - 1A down the live must return as 1A up the neutral. A 30mA device will trip at a 30mA difference.

Are you sure the harmonics return by the earth???

Try unpluging a few other things live the TV, computers etc - anything with a filter on the circuit. These devices cause leakage and can take you close to the operating figure of the RCD. Now try your light.

Do a 30mA test on the RCD.

If the fault is still there bin the light. Your RCD is trying to tell you something.

Register to Reply
Register to Reply 13 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

AW (2); bravo88 (1); Crabtree (1); electricalexpert65 (1); EXPAT07 (1); Keith Grewar (1); rishikathirasan (1); rssahni (1); senthilnair (2); silverfox (1); Wal (1)

Previous in Forum: Step Voltage?   Next in Forum: DC Solinoid

Advertisement