07/09/2012 8:06 PM
What is multiplication factor of a wattmeter?
Re: muliplication factor.
07/09/2012 8:23 PM
What watt meter?
Re: multiplication factor.
07/09/2012 8:24 PM
The multiplication of any meter is the number used to convert the displayed value into the actual measured value.
Re: Multiplication Factor
07/10/2012 2:33 AM
Multification factor =VA/max scale deflection=W*PF/max scale deflection
Multiplication factor of wattmeter is used to determine accurate reading of meter with respect to meters scale deflection.
02/22/2014 3:21 AM
Dear Friend,
The Power generation of high capacity, will have 11 KV, Voltage Level and Current will be in large value.
In order to measure the Power, a Potential Transformer and a Current Transformer is used. The Metring Voltage will be 110 volts, and the Secondary Current Rating for the Current Transformer will be 5 Amps. Hence Multiplication Factor comes into picture.
So the Factor for Potential Transformer voltage is 11000/110 = 100. Similarly for the Current Transformer - Let us say the Full Load Current of Alternator is 500 Amps at 11 KV, then the Factor is 500/5 = 100. The Watt Meter will measure at 110 Voltage and 5 Amps and indicate the Power and hence the Power measured by this Meter to be multiplied by 100 x 100 = 1,000.
DHAYANANDHAN.S