Hi everyone,
I have a question regarding capacitor banks.
Suppose you place a capacitor on a 10 KV meshed network, that is being radially operated. Now, when there is some kind of disturbance/failure that leads to service restoration. Is your bank gonna overcompensate or cause any harm to customers?
Hope you understand the problem.
Pathfinder Tags: capacitor reactive compensation
Re: Capacitor Problem in Case of Service Restoration?
07/10/2012 8:01 AM
If the capacitor is there to tune-out the reactive currents in the feeder upstram of it, then it shouldn't have much effect elsewhere unless it remains in-circuit with the fed equipment on that feeder out-of-circuit on power-up. Even then, it won't do any harm.
07/10/2012 8:17 AM
thank you ....that is exactly what i concluded from a few simulations. However, how can you prove it mathematically?....another question , suppose you use the "1/2KVar rule" suggested by grainger/lee which states that the capacitor must be placed optimally on a point where the var are equal to half the capacitor rating. With the intention to produce half of Kvar requirement upstream and half downstream. If i understood this , you will always overcompensate with this rule?or am i looking at this the wrong way.........
07/12/2012 11:44 AM
simpler question: At what extent does a fixed capacitor cause overvoltages?are overvoltages a direct result of overcompensation?