Anonymous Poster #1

Panel Short Circuit Rating

07/12/2012 7:51 AM

The short circuit rating for a MDB was 50KA for 1 sec. the panel has one incomer MCCB and 35 outgoing MCCB. i selected incomer MCCB with breaking capacity 50KA and outgoing capacity 36KA. Brand Schneider Electric NSX series MCCB.

the client after going through the SLD submitted by me, asked to change the outgoing breaking capacity to 50KA. so i told them since the incoming breaker is a current limiting device, there is no necessity to go for bigger capacity breakers in the outgoings. By the procedure of cascading i have selected the right components.

But the client is not accepting this.....so my question is whether this cascading is approved by IEC...Schneider says so, but no exact data on the approval...Does anybody know about this?

thank u

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Anonymous Poster #2
#1

Re: panel short circuit rating

07/12/2012 8:04 AM

Hi everybody

you select the breaking capacity for the incomer to be 50 KA for 1 sec which supposed to protect MDB and as soon as we know that a discremination time difference between the incoming and outgoing must take place as a preventive protection action your selection is good but in some industrial application it is required as your client required to be the same breaking capacities due to various types of highly inductive loads

Best Regards

Reply
Anonymous Poster #3
#2

Re: Panel Short Circuit Rating

07/12/2012 12:06 PM

Just because you have a breaker rated for 50 ka in the MDB does not prevent the fault current of 50 ka from occuring at the breaker rated at 36 ka. I assume the two breakers are in the same panel and the distance between them is small. Does the main breaker have some current limiting feature?

Reply
2
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: Panel Short Circuit Rating

07/12/2012 3:48 PM

Schneider are right to say no in this particular case.

If the customer requires the complete MDB to be rated at 50kA for 1 second then theoretically a short circuit on any one of the 35 outgoing MCCB feeders could result (in some situations) in a fault current of up to the full fault current (50kA).

Protection discrimination doesn't work the same way for short circuit current as it does for fuse ratings and curves, the incoming breaker is a current limiting device but NOT a fault current limiting device.

Unless you can prove that the prospective fault current directly after every one of the 35 MCCBs will never go above 35kA (which it only won't if there is enough line inductance or some form of short circuit limiting device in the circuit - which I seriously doubt) then you are stuck with having to change them to 50kA types.

If this was a separate downstream sub board located a fairly long cable distance after the MDB you would possibly be ok with lowering the fault rating of the MCCBs (site specific), but in the same MDB you are stuck and will need to change your MCCBs.

__________________
jack of all trades
Reply Good Answer (Score 2)
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#4

Re: Panel Short Circuit Rating

07/12/2012 10:54 PM

Friend,

I believe you are talking about "series ratings", but there is not enough information to be sure. Various manufacturers do have test results to show that a specific model of MCCB can be used to provide fault current protection to lesser-rated branch breakers. The NSX series is pretty intelligent, so it wouldn't surprise me if there is this sort of rating. You will have get a rating in writing from Schneider, with certain limits to settings or components.

--JMM

Reply
Associate

Join Date: Jul 2011
Posts: 48
Good Answers: 1
#5
In reply to #4

Re: Panel Short Circuit Rating

07/13/2012 3:44 AM

Please confirm which MCCB's are used, we would need to know the incomer plus the largest outgoing and smallest outgoing.

Schneider do produce tables to confirm if cascading is achieved.

There is nothing in IEC 61439-2 that restricts this practice, however it may be your client who restricts it, since if you have a short circuit in one circuit you will loose the entire board of 35 circuits which may not be acceptable. This is normally the reason for pushing to get full discrimination.

Out of interest have you carried out full design verification to IEC 61439-2 on this assembly design?

Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#6

Re: Panel Short Circuit Rating

07/13/2012 6:21 AM

there is a difference between discrimination where a small breaker trips before a larger one and cascading. The upshot is if the smallest device sees the full fault level for a very small time it must be able to contain it all be it unusable afterwards. Merlin Gerin / Schneider produce cascade tables where they show which device will cascade with another. Obviously if you have mixed manufacturers you will be goosed for getting the test information. This information might sway your client.

Cascade tables are produced by most reputable manufacturers but each device is not shown and its generally hard work.

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7

Re: Panel Short Circuit Rating

07/13/2012 11:18 PM

No question! Your outgoing MCCBs must also be rated for 50kA only.

Reply Score 1 for Off Topic
Associate

Join Date: Jul 2012
Posts: 39
#8

Re: Panel Short Circuit Rating

07/14/2012 5:36 AM

With the exception the mdb is for a peculiar application, i'll say your client is a contractor who knows little or too well of what he is requesting. And Schneider will say no to keep on the safe side of everything but economic feasibility of your panel.

Reply
Reply to Forum Thread 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

3PhaseDesign-Craig (1); Anonymous Poster (2); AW (1); electricalexpert65 (1); jack of all trades (1); jmueller (1); silverfox (1)

Previous in Forum: Switchgear   Next in Forum: Lightening Arrestor or Voltage Stabilizer

Advertisement