The short circuit rating for a MDB was 50KA for 1 sec. the panel has one incomer MCCB and 35 outgoing MCCB. i selected incomer MCCB with breaking capacity 50KA and outgoing capacity 36KA. Brand Schneider Electric NSX series MCCB.
the client after going through the SLD submitted by me, asked to change the outgoing breaking capacity to 50KA. so i told them since the incoming breaker is a current limiting device, there is no necessity to go for bigger capacity breakers in the outgoings. By the procedure of cascading i have selected the right components.
But the client is not accepting this.....so my question is whether this cascading is approved by IEC...Schneider says so, but no exact data on the approval...Does anybody know about this?
thank u