Lightening Arrestor or Voltage Stabilizer

07/12/2012 7:52 AM

At our construction project site, it was identified that main incomer 3 phase supply for all control panels are having voltage fluctuations at several intervals. Resulting to that on the same day, we found our crane control panel wiring damaged.The reason behind this damage is not identified but there was short circuit in 11kV line near the site before damage.

Will voltage stabilizer or UPS supply for all the control panels do good for safe operation of the control panels at the project site. OR do we require to place lightening arrestors/ surge suppressors at the site? (The site is located at very high altitude in the Himalayas). Any help in this regard is highly appreciated. Thank you.

__________________
Creativity guaranteed!!!!!
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#1

Re: Lightening Arrestor or Voltage Stabilizer

07/12/2012 9:34 AM

What kind of damage occurred in the control panel?

A major cause of burnt insulation is loose connections where the wire attaches to some distribution point. It may also cause very significant wire oxidation.

Your 3 wire-three phase power will have no ground wire until you transform it from a delta configuration to a wye configuration. Then, if you have significant ground current, it is most likely due to an imbalance.

What is your panel voltage level?

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Active Contributor

Join Date: Jun 2011
Location: India
Posts: 12
#3
In reply to #1

Re: Lightening Arrestor or Voltage Stabilizer

07/18/2012 12:55 AM

Thanks for ur reply.

The wires were burnt.

There were no loose connections as far as observed.

The panel voltage level is 230V.

__________________
Creativity guaranteed!!!!!
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#2

Re: Lightening Arrestor or Voltage Stabilizer

07/13/2012 1:22 AM

Yes, Yes and Yes.

Sorry friend. There is no simple and single solution to power quality at your remote location. Your suspicion on the short on the 11kV line is well iustified. But, so would be nearby lightnings anywhere from the generator to you. Which may be many hundreds of kilometers.

Spikes may be limited in several steps. Spark gaps to limit the most brutal overvoltages. Like 10kV spike on a 220V line. A choke on every phase, to kill high frequency parts of the disturbancy. MOV blocks to absorb, what still gets thru. It is all for spikes that can an will damage electrics and cabling. MOV blocks are Zinc Oxide ceramic bricks that are capable of absorbing spikes frequently present on the power lines. They are replaceable. They are sized to max. voltage: 110V average = 110/0,7 = 157V peak. The MOV I would select is in the range 180-220V, that it would turn on only on really excessive voltages. A fist or two fist size block would protect your equipment. You fabricate your own, I am not aware off the shelf assembly.

You need more? Write!

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2011
Location: India
Posts: 12
#4
In reply to #2

Re: Lightening Arrestor or Voltage Stabilizer

07/18/2012 12:58 AM

Thanks for your reply.Yes I understand that.

__________________
Creativity guaranteed!!!!!
Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

leveles (1); NotUrOrdinaryJoe (1); sash46 (2)