Dear ALL,

For On Off Valve Full Port Ball Valve Type , While preparing specsa ,is it customary to specify Rated Cv

Regards

Jose

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Rated Cv

07/13/2012 6:18 AM

As the valve is on/off, and full bore, there is absolutely no reason to specify Cv.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 3)
Power-User

Join Date: Mar 2008
Location: Mumbai
Posts: 250
Good Answers: 2
#2
In reply to #1

Re: Rated Cv

07/14/2012 6:36 AM

Thanks

Register to Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#3

Re: Rated Cv

07/14/2012 11:51 AM

to the point - GA

Register to Reply
Active Contributor

Join Date: Apr 2007
Location: Los Angeles, CA
Posts: 19
#4

Re: Rated Cv

07/15/2012 1:00 PM

All valves have a Cv and if purchasing/specificing a valve, state the Cv.

Otherwise, how does one know if it will work?

A slurry will have a different flow rate (Cv) than water.

Be a smart engineer and specify the Cv.

Register to Reply
Power-User

Join Date: Dec 2010
Location: Tulsa, OK
Posts: 184
Good Answers: 2
#5

Re: Rated Cv

07/16/2012 9:33 AM

All valves have a rated Cv but for on off purposes, you only need to know the general Cv for the line size valve you will be choosing.

But be careful that the valve is sized for the correct maximum flow, in other words make sure the maximum flow of the valve can handle your design throughput.

Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

artonpaper (1); Iris (1); josej (1); PWSlack (1); vargaalex (1)

Previous in Forum: Estimating Orifice Plate Installed Accuracy for Turn Down Operation   Next in Forum: Calculation for Total Air Flow in Boiler

Advertisement