IR Testing Using DAR (Dielectric Absorbtion Ratio) Time Mode

07/14/2012 3:45 AM

Hi All,

I have testing insulation resistance for 3 phase induction motor by using DAR mode. Based on table attached show the value less than 1 = poor, 1-1.4 = questionable, 1.4-1.6 = ok and above 1.6 = good insulation. The situation I faced now is the result for good motor (new) and bad motor showed same result = 1.2 which mean in marked 'questionable'. for your information the motor in star connection, voltage rated = 440 V 50 Hz. How I am to be sure the tested motor is in good condition by using DAR mode. What the different between DAR mode & PI mode? Is it the same function to verify condition for insulation resistance? Please help me to verify this problem. thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Sep 2011
Location: Near the New Madrid Fault. USA
Posts: 269
Good Answers: 1
#1

Re: IR Testing Using DAR (Dielectric Absorbtion Ratio) Time Mode

07/16/2012 11:43 AM

Google " IEEE standard 43-2000" and pick a site, that will help you understand PI.

__________________
It's not Rocket Science
Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#2

Re: IR Testing Using DAR (Dielectric Absorbtion Ratio) Time Mode

07/17/2012 9:39 AM

Dear zhafran,

DAR(Dielectric Absorption Ratio) is the ratio of reading of insulation resistance values measured after 15 secs. and after 1min.(60secs.).The DC TEST VOLTAGE MUST BE CONTINUING during the whole period of measurement; at the end of the test,the DAR value can be calculated or directly displayed by the test equpment. Similarly,PI(Polarisation Index) is the ratio of Insulation Resistance values maesured after 1min.(60secs.) and 10min.(600secs.)The DC TEST VOLTAGE MUST BE CONTINUING during the whole period of measurement; at the end of the test,the PI value can be calculated or directly displayed by the test equpment.

Actually,when you are injecting DC voltage to the motor for the above testing , capacitance formed due to the insulation system, is charged up. It is to be noted that,the capacitane has to be charged up in the first 15 secs time in case of DAR mode and similarly in PI mode, capacitance has to be charged up in first 1min.(60secs.) time. Therefore, the ratio of IR values in the the above two type of tests(depending on formation of capacitances/charging of capacitor, vis-a-vis,alingnment of positive and negative charges towards negative and positive plates respectively). So by this measurements,condition of insulation system can be monitored.

Thanks,

Manindra