245 kV Circuit Breaker Question

07/15/2012 10:49 AM

why 245 kv circuit breaker not a gang operated

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: 245 kV Circuit Breaker Question

07/16/2012 10:29 AM

Usually the three poles on 245kV or higher breakers are such a long distance apart (to meet phase spacing requirements) that the operating shafts would be too long for one mechanism to move 3 sets of contacts consistently in the short time required for tripping or closing. Therefore a separate operating mech is used for each pole.

138kV is about the limit for having all three poles on one common frame with one mechanism to operate them. The lengths of the bushings give enough spacing to provide the necessary phase spacing at that voltage.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#2
In reply to #1

Re: 245 kV Circuit Breaker Question

07/16/2012 11:12 AM

I have seen 34.5kV SF6 CB (BBC) operated by 3 separate motor operated mechanisms made by Color Emag in 1981.

__________________
pnaban