Intellipower 1.6KVA UPS Issues

07/16/2012 2:04 AM

Hi all,

I recently installed a UPS on my house circuitry. The UPS installed is Intellipower 1.6KVA UPS. The UPS batteries had failed so i had them replaced. After that the output voltage was proper (110 VAC). Since the voltage levels required for my circuitry is 240VAC so i had an auto-transformer installed on the UPS output. After the installation i checked the voltage which was 240V. The problem i am facing is that even with the power mains available (UPS bypass mode) the circuit fails to power up. I checked this by switching on a 22W flourocent light and it just flickers furthermore upon switching on a fan ( 80-120W) the flourocent light just dies out. What could be the issue here.

Any help would be greatly appreciated.

Regards

Register to Reply
Pathfinder Tags: Intellipower ups
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#1

Re: Intellipower 1.6KVA UPS Issues

07/16/2012 6:23 PM

Nightshade,

If you have put a transformer in to raise the voltage, you have cut the available current.

The Voltage and Current are reciprocal to each other when you introduce a transformer.

1.6kVA/110V = 14.5A therefore @ 240V: 1.6kVA/240V = 6.7A

Not really enough to drive much, especially considering losses just to run the transformer itself.

Better to get the right sized UPS at the right voltage output.

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
Associate

Join Date: Nov 2011
Posts: 48
#2
In reply to #1

Re: Intellipower 1.6KVA UPS Issues

07/17/2012 12:08 AM

I dont think the currents are less to drive anything. It depends on the Wattage of the connected load.

As an added development i tried plugging in a lamp right at the output of the transformer and it woked perfectly. This means that the UPS wiring has been messed up.

Regards

Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#4
In reply to #2

Re: Intellipower 1.6KVA UPS Issues

07/17/2012 12:55 AM

Nightshade,

Your understading of how this works is flawed, the Rated Voltage and Current requirements are the key to any electrical device working properly.

Just because a device is rated at 240W does not mean it will work on any power.

The device will be rated to operate at a specified Amps at a specified Voltage.
Changing either value does not mean it will still work just because the Wattage is the same.

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
Associate

Join Date: Oct 2009
Posts: 26
Good Answers: 1
#3

Re: Intellipower 1.6KVA UPS Issues

07/17/2012 12:30 AM

Dear Nightshade,

I understand that the fan and light are working when the UPS giving power by battery (back up mode) but these doesn't works when power available on UPS input terminals.

This case, the possibility is your input power supply to the UPS is not rate voltage, I mean it should less than 240V. Check and clear it.

Byee

Register to Reply
Associate

Join Date: Nov 2011
Posts: 48
#5
In reply to #3

Re: Intellipower 1.6KVA UPS Issues

07/17/2012 2:03 AM

Dear Sukumar75

The light worked when the UPS was in bypass mode ( power mains available) and not in the backup mode since the batteries required charging. I will charge the batteries and see the output.

As for the earlier comment i agree both voltage and current ratings need to met. I checked the rated voltage of the lamp which is 220-2440VAC and net power is 22W.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6

Re: Intellipower 1.6KVA UPS Issues

07/17/2012 2:25 AM

Does your transformer work correctly when it is plugged directly to mains and not using the bypass mode of the UPS at all?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Associate

Join Date: Nov 2011
Posts: 48
#7
In reply to #6

Re: Intellipower 1.6KVA UPS Issues

07/17/2012 2:51 AM

I have not tried testing the transformer directly from the power mains since its a step up auto-transformer ( 110-220 V). I was not sure it could sustain the increased voltage level of 440V if plugged directly from power mains.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#8
In reply to #7

Re: Intellipower 1.6KVA UPS Issues

07/17/2012 4:55 AM

Your utility power is 220V and your UPS is 110V?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Associate

Join Date: Nov 2011
Posts: 48
#9
In reply to #8

Re: Intellipower 1.6KVA UPS Issues

07/17/2012 5:34 AM

Yes indeed it is so. The input is auto selected by the UPS and can be either 110V or 220V however the output is 110V thus i have connected a transformer to step this voltage up to 220VAC.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#10
In reply to #9

Re: Intellipower 1.6KVA UPS Issues

07/17/2012 6:22 AM

So your UPS auto senses the incoming and fixes the output at 110 regardless of incoming.

and when you go to bypass mode the UPS does what? pass the mains straight through (could be a problem) or pegs it at 110 in a not really a true bypass kind of way?

Do you have a multimeter?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Associate

Join Date: Nov 2011
Posts: 48
#11
In reply to #10

Re: Intellipower 1.6KVA UPS Issues

07/17/2012 9:29 AM

The UPS is an inline type so the power is always routed through the batteries. The ouput is always 110V

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#13
In reply to #11

Re: Intellipower 1.6KVA UPS Issues

07/17/2012 10:31 AM

So there is no bypass?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#14
In reply to #11

Re: Intellipower 1.6KVA UPS Issues

07/17/2012 5:04 PM

nightshade,

Given the information Wal has been able to get, you have the wrong UPS for the wrong environment.

If your mains is 240V get a 240V UPS. What you are doing is dangerous.

Unsubscribing now.

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
Associate

Join Date: May 2010
Posts: 46
Good Answers: 1
#12

Re: Intellipower 1.6KVA UPS Issues

07/17/2012 9:29 AM

Is it possible for you to show a block diagram of the connections you have made ( showing the mains, the UPS, the transformer and the lamp)? Do you get 220 v at the transformer output when the input supply to the UPS is removed?Do you get a 110v output at the UPS when you remove the transformer and also the input supply to the UPS? Does the output supply fail only when you connect the input supply to the UPS? It might be possible to draw some conclusions if you could answer these.

Register to Reply
Associate

Join Date: Nov 2011
Posts: 48
#15
In reply to #12

Re: Intellipower 1.6KVA UPS Issues

07/18/2012 12:03 AM

Thanks guys for you feedback. Firstly there is nothing dangerous about using a UPS transformer combination for back up. Secondly i rectified the problem which was due to neutral fault.

Now comes the interesting part. The UPS previously worked fine in back up mode but now even after charging it for 8 hours the batteries are not charging up. I need help with rectifying this issue first

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#16
In reply to #15

Re: Intellipower 1.6KVA UPS Issues

07/18/2012 9:22 AM

New batteries right?

How many, what type and did you connect them properly?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Associate

Join Date: Nov 2011
Posts: 48
#17
In reply to #16

Re: Intellipower 1.6KVA UPS Issues

07/18/2012 9:31 AM

The batteries are 12V 8Ah each and yes they are brand new. The problem here is that the front panel is not working as it should. Moreover there is no manual available for the UPS on the internet so i am flying blind here. Now i can connect it to a PC using RS232 and a RUPS software i am gonna try that first

Register to Reply
Register to Reply 17 comments