Electrical Eng ( MCC Utility Consumption)

07/17/2012 9:27 PM

i have a ventilation fan motor rating is 1. 1 kw. can i use the mcc feeder below then the motor rating or above then this motor rating pls advise ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Electrical engg ( MCC utility consumption)

07/17/2012 9:49 PM

Depends. What do you want to protect?

Register to Reply
Participant

Join Date: Jul 2012
Posts: 2
#2
In reply to #1

Re: Electrical engg ( MCC utility consumption)

07/17/2012 10:21 PM

i have ventilation fan 1.1 kw motor rating !

how to size a mcc feeder for this motor rating ?

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#4
In reply to #2

Re: Electrical engg ( MCC utility consumption)

07/18/2012 2:19 AM

When you select the components of a motor feeder say SCPD (i.e. MCCB), contactor and overload relay it has to comply with the requirements of Type-2 coordination of IEC 60947. Every manufacturer will provide in his product catalogue the selection chart for components to match with the KW rating of the motor. For high inertia equipment like fans etc. overload relay selected should take care of higher starting time of motor.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Electrical engg ( MCC utility consumption)

07/17/2012 11:16 PM

<un subscribe>

Register to Reply
Register to Reply 4 comments
Copy to Clipboard

Users who posted comments:

debata07 (1); lyn (2); narendranei5 (1)

Previous in Forum: Machine Safety Standards   Next in Forum: Transformer Oil

Advertisement