Transformer Oil

07/18/2012 4:59 AM

In a 400/6.6 KV x-mer, oil experience voltage upto 400 KV between phase and potential diff between Ht-LT is also high but during BDV test oil break-downs only at 80 KV , How ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster #1
#1

Re: Transformer Oil

07/18/2012 5:02 AM

Water.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Transformer Oil

07/18/2012 6:58 AM

The distance between the electrodes in a break down test is much smaller than you would find in your transformer. Therefore you will get a figure along the lines of XXKV/cm.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Transformer Oil

07/29/2012 9:44 AM

80kV Breakdown voltage is across a gap of about 2.5mm. Whereas within the transformer tank, you have much larger gap between the live winding and the earthed tank.

Register to Reply
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (1); TonyS (1)

Previous in Forum: Electrical Eng ( MCC Utility Consumption)   Next in Forum: Required Electromagnet Design Calculation

Advertisement