why do the standard consider 3 Seconds for short circuit withstand current of 63/20KV Substation,and 1 Second for 400, 230KV Substation?
why don't we consider 1 Second for 63/20KV Substation?
Re: power Electrical Engineering
07/21/2012 7:42 AM
Which standards did you get that from?
Good Answers: 804
07/21/2012 10:55 AM
Because if you have a fault at the 400V tier, and it takes 1 second for the 400V protective device to clear it, the higher tier system has to stay in a little longer, otherwise the fault interruption spreads further. But at the 230kV tier, it is assumed there is a lot of impedance between it and any possible down stream fault so a lower tier fault will be dampened, but if a fault happens AT the 230kV tier, you want to clear it fast.
Good Answers: 104
07/21/2012 11:19 AM
You wouldn't happen to be Anonymous Poster, would you?
http://cr4.globalspec.com/thread/79349/Electrical-Engineering
Re: Power Electrical Engineering
07/21/2012 7:33 PM
rule of thumb: fault clearing time == 2-3 cycles for almost all systems.
E pur si muove -- Galileo
Good Answers: 170
07/29/2012 9:04 AM
Which Standard says so?