TNS System

07/22/2012 1:46 PM

Hello Gurus,

The customer owned the padmounted xformer and we use the 3phase, 5W system going to distribute to the loads. Is there a danger of broken neutral in this type of system and where the location is lightning prone it is not advisable to use TNS system because of the danger of burning neutral instead TT is advisable?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: TNS system

07/22/2012 4:35 PM

If there is a broken neutral anywhere on any earthing network, then expect some single phase loads to go phut, Uncle. That is why the electricians do a special check on new installations before energising them, and periodic re-inspection.

__________________
Good moaning!
Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#2

Re: TNS system

07/22/2012 4:55 PM

By the way, did you read the articles about earthing systems before posting here?

__________________
Good moaning!
Reply
Participant

Join Date: Jul 2012
Posts: 4
Good Answers: 1
#3

Re: TNS System

07/23/2012 4:59 AM

In a TT earthing system, the protective earth connection of the consumer is provided by a local connection to earth, independent of any earth connection at the generator or transformer.

The big advantage of the TT earthing system is that it is clear of high and low frequency noises that come through the neutral wire from connected equipment. TT has always been preferable for special applications like telecommunication sites that benefit from the interference-free earthing. Also, TT does not have the risk of a broken neutral.

In locations where power is distributed overhead and TT is used, installation earth conductors are not at risk should any overhead distribution conductor be fractured by, say, a fallen tree or branch

In TN, an insulation fault is very likely to lead to a high short-circuit current that will trigger an overcurrent circuit-breaker or fuse and disconnect the L conductors. With TT systems, the earth fault loop impedance can be too high to do this, or too high to do it quickly, so an RCD (or formerly ELCB) is usually employed. The provision of a Residual-current device (RCD) or ELCB to ensure safe disconnection makes these installations EEBAD (Earthed Equipotential Bonding and Automatic Disconnection). Earlier TT installations may lack this important safety feature, allowing the CPC (Circuit Protective Conductor) to become energized for extended periods under fault conditions, which is a real danger.

http://en.wikipedia.org/wiki/Earthing_system

CR4 Admin: Modified Post

Copyright Violation: Reduced copied text according to copyright law. Please see Section 12 of the CR4 FAQ about posting copyrighted material.

Reply Score 1 for Good Answer
Reply to Forum Thread 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!

Previous in Forum: Bi-Voltage Induction Motor   Next in Forum: Generator Transformer Phase Sequence Problem RYB-BYR

Advertisement