Fire Pump Calc

07/26/2012 11:37 AM

Owner has an original 25 stories building project which has a fire pump design under IFC and IBC codes (NFPA). Now he wants to duplicate building next to original. Question is: Shall fire pump design be reviewed (capacity duplicated) to service additional building hazard (coincidence of hazard events) in additional building?

I can not find any article in referred codes to address this specific case.(I consider that pump should remain the same as worst case hazard would not happen at both bulidings at same time).

Register to Reply
Pathfinder Tags: fire pump
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Fire pump calc

07/26/2012 11:55 AM

Did you not hear what happened to the Twin Towers?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Nov 2008
Posts: 18
#2
In reply to #1

Re: Fire pump calc

07/26/2012 12:22 PM

Thanks JohnDG, that would be in line with duplicating capacity. Is there a revision of the IFC/IBC regarding this?

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Fire pump calc

07/26/2012 12:44 PM

This question can only be answered by a Civil Engineer.

That engineer will be familiar with the local codes and requirements.

Since we don't even know what country you are in, it is foolish to expect an intelligent answer to such a broad question.

You are not considering using one system to protect both buildings, right?

You DO have an engineer working on this project, don't you???????

Register to Reply
Active Contributor

Join Date: Nov 2008
Posts: 18
#4
In reply to #3

Re: Fire pump calc

07/26/2012 12:57 PM

Lyn, yes we have a civil engineer working and also others. Original buliding is protected according local codes and requirements, that is fully sprinklered and fire pump and tank. New building shall be identical. Local codes do not call for addittional pump and water capacity if building is same owner (condominium like). I personally think it would be wise to assume new building would impose addittional concurrent hazard.

Register to Reply
Guru

Join Date: Aug 2007
Location: London England.
Posts: 583
Good Answers: 10
#9
In reply to #4

Re: Fire pump calc

07/27/2012 5:50 AM

To hell with local codes, treat it as a separate building,use all the latest safety equipment, and personally on a 25 story I'd like to see at least two storage tanks in the building,one at the top & one midway so that your not relying on power pumps that may fail.contry to the film companies, not all sprinklers come on at once like they do in films, only the ones directly in the field of the fire, so you're not dumping tons of water all at once, so a steady flow is whats needed, the initial pressure is by compressed air on the tank, which gives time for fire services to hook up and start replenishing the water and pressure in the tanks.

Bazzer.

__________________
When I die I'd like to go peacefully in my sleep like my dad,not shouting and screaming like his passengers.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Nov 2008
Posts: 18
#10
In reply to #9

Re: Fire pump calc

07/27/2012 10:21 AM

Thanks Bazzer Englander for your comments. We are already proposing a booster pump midway to the building top to ease the burden on the main pump located in the basement where the firewater tank is located. Both buildings are designed with state of the art fire protection technology and will propose a pump/controller scheme for each building with a backup transfer manifold in the event of maintenance/failure of one of the pumps.

Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#5

Re: Fire pump calc

07/26/2012 1:30 PM

Your system overall must be designed to supply adequate water to the largest hazard zone at the most remote hydraulic location. One pump connected to two buildings is a single system.

If the water supply line from the pump to the new building is the same length, and the sprinkler system design for the new building is a mirror image, you should not even need to provide new design calculations.

The only possible fly in the ointment is your local code officials. If they allow a single pump to supply both buildings (most will), you are on solid ground in terms of design.

On the other hand, as a professional, I would recommend against such a design if the buildings were within 100 feet of each other. The cost of an additional pump will be chump change compared to the building.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Nov 2008
Posts: 18
#6
In reply to #5

Re: Fire pump calc

07/26/2012 1:54 PM

Thanks WJMFIRE, you are in line with out thinking, excess cost for additional pump is nics compared to new building TIC.

Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#7
In reply to #6

Re: Fire pump calc

07/26/2012 2:11 PM

I belong to a forum of Building Code officials, and I took the liberty of asking your question there. The consensus (so far) is that it is probably allowable to use only one pump, but this guy makes a very good observation:

"The existing fire pump could serve both buildings if properly sized. However, you need some agreements and easements in place so that if one... building is sold, that the fire pump in the existing building will continue to serve it."

__________________
Semper Ubi Sub Ubi
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Nov 2008
Posts: 18
#8
In reply to #7

Re: Fire pump calc

07/26/2012 2:22 PM

Thanks Doorman, good comment to include in owner documents.

Register to Reply
Guru

Join Date: Aug 2007
Location: London England.
Posts: 583
Good Answers: 10
#11
In reply to #7

Re: Fire pump calc

07/27/2012 11:04 AM

Another reason to have two pumps, If you sell one building and the new owner wants to flatten it you've then got to start retro fitting a new pump which is always more expensive, with two pumps there is backup, & lets face it sods law says when you most need it it breaks down.

Bazzer

__________________
When I die I'd like to go peacefully in my sleep like my dad,not shouting and screaming like his passengers.
Register to Reply
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

aguilafede (5); Bazzer Englander (2); Doorman (1); JohnDG (1); lyn (1); WJMFIRE (1)