Sensitive Earth Fault Protection Relay

07/31/2012 6:53 PM

if the network is not earthed.

is the SEFR will work when the fault occure in that n/w?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Sensitive Earth Fault Protection Relay

08/01/2012 3:16 AM

Check out the Wikipedia article on earthing, in particular IT systems.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#2

Re: Sensitive Earth Fault Protection Relay

08/01/2012 5:54 AM

Obviously.

For this, your unearthed system should have a neutral earthing transformer or a zig zag transformer having star connected primary winding with neutral terminal brought out for connecting to earth through an arc suppression coil ( Peterson coil ).

All the out going feeders of such a system should have a core balance current transformer ( CBCT ) through which,the 3 core armoured power cable( or single core cbles of all the 3 phases ) pass . The SEFR should be connected across the secendary terminals of this current transformer of respective outgoing feeder.

This arrangement is meant for protecting the feeder under single phase to ground fault conditions in the unearthed or non-effectively earthed powersystem.

__________________
Learning is a never-ending process.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Sensitive Earth Fault Protection Relay

08/29/2012 10:39 AM

If it is a numerical relay with zero sequence current sensing, then YES!