Higher Rating of CTs

08/02/2012 2:39 AM

Hi All,

I have a 220 KV GIS and using metering CTs of 150/1. I am drawing a current of about 30 Amperes. I wish to know whether this has any impact on the accuracy of the energy recording. What data/chart (apart from routine test report) should I ask the manufacturer to derive the accuracy, particularly at lower currents?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: Higher rating of CTs

08/02/2012 8:58 AM

If they are actually metering grade CTs, then they should be most accurate in the lower end of their range. Your current of 30A is close to 25%, so that is good.

The CT manufacturer's specifications and factory test report should give you all you need to be assured of their accuracy. However, I don't know of any good way to make "adjustment" in the field for variation in CT accuracy. The critical item is calibration of your energy meter. It is more often the source of greater error.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Participant

Join Date: Dec 2011
Posts: 4
#2

Re: Higher Rating of CTs

08/03/2012 12:24 AM

Dear friend,

First tell me what is accuracy class of this CT ?

If it is Cl. 0.5 for metering, % error will be +/-0.75% at 20% load instead of +/- 0.5% error at 50 to 100% load. you should choose CT 120% of rated full load current.

Register to Reply
Active Contributor

Join Date: Nov 2008
Posts: 13
#3
In reply to #2

Re: Higher Rating of CTs

08/03/2012 1:52 AM

Sorry...I have not mentioned Accuracy class...it is 0.2FS5;

Further, I wish to know whether, there is any curve/graph which shows the accuracy at different currents. What is 'Bell Curve' in this context?

Register to Reply
Participant

Join Date: Dec 2011
Posts: 4
#4
In reply to #3

Re: Higher Rating of CTs

08/03/2012 2:58 AM

Kindly write class according to core of CT and VA rating.

Register to Reply
Participant

Join Date: Dec 2011
Posts: 4
#5
In reply to #3

Re: Higher Rating of CTs

08/03/2012 3:05 AM

According to Cl 0.2,

at 20 % load of 150=30A

% error will be +/-0.35. and if load is goes to 5% then % error will be +/-0.5 instead of 0.2.

Register to Reply
Commentator

Join Date: May 2011
Posts: 84
Good Answers: 1
#6
In reply to #3

Re: Higher Rating of CTs

08/03/2012 10:06 AM

i dont know what you meant by 0.2FS

but if it is 0.2S class CT, then it's magnetic core is made up of mumetal instead of crgo.

therefore, at lower currents also, it will give + or - 0.2% error.

rest assured your CT is working fine and within error limits

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

hariombaboo (3); muditmah (1); PeterT (1); Sadanand Jadaye (1)