Generator Field Circuit Breaker Fault

08/02/2012 2:45 AM

the field circuit breaker contact in the path of discharging resistance got damaged during closing.

what is the possible reason of damaging of this contact during closing.

what are the risk faced by field breaker and generator rotor/ stator windings without this discharging/ arc quenching resistor.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: generator field circuit breaker fault

08/02/2012 3:08 AM

Without being able to see the installation from here, one of the possibilities is that the contact closed onto a short circuit.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#2

Re: Generator Field Circuit Breaker Fault

08/03/2012 3:13 AM

The discharge resistor function is to discharge the stored energy in the field windings to earth when the main field CB is open.

Thus, the contact in field discharge resistor circuit shall close after the main FCB opens and shall open before the FCB closes.

It could be that the contact timing is not OK (didn't open before the FCB closed) and that resulted in damage to the contact.

__________________
Raghunath
Register to Reply Score 1 for Good Answer