Why REF is Tripping Beyond Its Zone of Protection?

08/02/2012 4:23 AM

My question is regarding REF protection...in one of the instances an earth fault has taken place in the LV busbar zone..however the REF Relay has tripped the circuit.As far as I know REF is used for specific zone protection i.e. in this case it is meant to protect the region from the transformer to the incoming busduct...why has REF tripped if a fault is outside its zone of protection..any help would be highly appreciated...

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Why REF is tripping beyond its zone of protection??

08/02/2012 5:19 AM

Clearly the premise that the REF is operating outside its zone of protection is wrong.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: May 2012
Posts: 20
#4
In reply to #1

Re: Why REF is tripping beyond its zone of protection??

08/02/2012 7:27 AM

Sorry I did not get the statement of the premise being wrong...can you elaborate

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: Why REF is tripping beyond its zone of protection??

08/02/2012 7:36 AM

The assumption that the fault is outside the REF's zone of protection is invalid?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Oct 2011
Posts: 34
#2

Re: Why REF is tripping beyond its zone of protection??

08/02/2012 6:00 AM

Kindly clear the following point :

Is it an high impedence REF circuit or low impedence REF Circuit .?

whether the fault has occured in the upstream end or down stream end?

Register to Reply
Active Contributor

Join Date: May 2012
Posts: 20
#3
In reply to #2

Re: Why REF is tripping beyond its zone of protection??

08/02/2012 7:25 AM

The protection is by means of low impedance numerical relays...and the fault has occurred downstream...I just basically want to know how should an REF react to an external fault....and are there any chances for e.g. incorrect polarity or use of different CT ratios etc. that shall cause it to trip on external faults

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #3

Re: Why REF is tripping beyond its zone of protection??

08/02/2012 7:37 AM

An earth fault would do it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Oct 2011
Posts: 34
#7
In reply to #3

Re: Why REF is tripping beyond its zone of protection??

08/02/2012 7:48 AM

Since it is a low impedence circuit , earth fault in the down stream will also cause a back flow of elctron in the transformer neutral . that might be reason of REF tripping .

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #7

Re: Why REF is tripping beyond its zone of protection??

08/02/2012 8:36 AM

Precisely. There is a current between either a phase or the neutral to earth. The REF is doing its job.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: May 2012
Posts: 20
#10
In reply to #7

Re: Why REF is tripping beyond its zone of protection??

08/03/2012 2:18 AM

Do you mean to say that low impedance numerical relays are highly unreliable when it comes to REF protection and that it shall always trip with faults outside its zone for e.g. somewhere in the downstream...or is there a way of using the numerical relays (Low impedance) and yet preventing the backflow of current to Xmer neutral??

Register to Reply
3
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#11
In reply to #10

Re: Why REF is tripping beyond its zone of protection??

08/03/2012 3:03 AM

Dear Kushal,

The issue can be cleared if REF protection stability test can be conducted. The REF protection, whether low impedance type or high impedance type, is a unit protection and shall be stable for out-of-zone faults. The reasons can be many:

  • One of the CTs not in circuit (could happen if the short across one of the CTs is not removed, this is the case typically with neutral CT)
  • CT polarity issues
  • CT ratio issues - in case of low impedance REF protection using numerical relays, the CT ratio mismatch can be corrceted by appropriate setting in the relay.
  • Multiple earthing of CT secondary wires - this is one of the common problems. All the 4-CTs should have earthing at one common point to avoid circulation currents.
  • In case of low impedance REF protection - pickup threshold and slope are important for stability and should follow the manufacturer's recommendation.

Once you find the cause, please provide feedback to the forum.

__________________
Raghunath
Register to Reply Good Answer (Score 3)
Active Contributor

Join Date: May 2012
Posts: 20
#12
In reply to #11

Re: Why REF is tripping beyond its zone of protection??

08/03/2012 5:09 AM

Thanks a lot!! that makes things a lot clear..!

Register to Reply
Commentator

Join Date: May 2011
Posts: 84
Good Answers: 1
#13
In reply to #12

Re: Why REF is tripping beyond its zone of protection??

08/03/2012 9:38 AM

we were disturbed by the same problem a while ago in our plant.

found out that nuetral CT was not in line. a short link was applied through it's terminals.

Register to Reply
Associate

Join Date: Jul 2011
Posts: 48
Good Answers: 1
#9

Re: Why REF is Tripping Beyond Its Zone of Protection?

08/02/2012 6:21 PM

I would check the CT positions and the location of the N Earth link to ensure it has been assembled correctly

Register to Reply
Register to Reply 13 comments