Class 0.3 CT for Revenue Metering

08/12/2012 1:50 AM

For one of the projects, i have used class 0.2 CT(Current transformers) for revenue metering, since class 0.3 was the requirement. Now do i have to use class 0.2 Energy meters for revenue metering? or can i use class 1 energy meters , since i have already chosen the correct CT.

thank you

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Class 0.3 CT for Revenue Metering

08/12/2012 8:53 AM

Ask your tutor!

__________________
The reports of my death are greatly exaggerated.
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Class 0.3 CT for Revenue Metering

08/12/2012 9:42 AM

Based on your logic, why not? That will give you greater accuracy.

Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#3

Re: Class 0.3 CT for Revenue Metering

08/13/2012 1:41 AM

Perhaps OP could tell us what the difference is between these classes....

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#4

Re: Class 0.3 CT for Revenue Metering

08/13/2012 5:17 AM

The class gives the value of the measuring error.

It has been a long time ago, but I think class 1 equals to 1% measuring error.

Class 0.2 equals to 0.2 % measuring error.

According this, you can not go for a class 1 measuring instrument (which will be cheaper ..);

A chain is as strong as the weakest point..

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Class 0.3 CT for Revenue Metering

08/21/2012 9:13 PM

You must use a class 0.2S (not even 0.2, I would say) for the CT as well as for the meter for tariff metering. But, well, as your spec. was Class 0.3, you have already gone for a better accuracy CT with your Class 0.2 CT. But, here only the CT will be accurate. If you "marry" a Class 1.0 Meter to this, the meter will still have its errors pertaining to its class. So, it is always better to have the meter & the CT of the same accuracy class.

Reply