08/12/2012 7:53 AM

In my ship to start one generator we are using 2 no of 12 volt batteries in series.At battery charging supply disconnected condition one battery shows 12.5 volts and another one shows 10 volts only.So that to start generator connect batteries with 26 volt dc supply from battery charger and at chargeable condiytion everytime we are starting the generator.If we continue this method any problem will be created to battery charger or to the good conditional battery ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: 12 volt battery charging

08/12/2012 9:22 AM

Replace the defective battery!

Register to Reply Good Answer (Score 3)
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#2

Re: 12 volt battery charging

08/12/2012 9:24 AM

Agree with ↑

Replace the defective battery!

__________________
Semper Ubi Sub Ubi
Register to Reply
Commentator

Join Date: Apr 2008
Location: Rhode Island, USA
Posts: 56
Good Answers: 5
#3

Re: 12 Volt Battery Charging

08/12/2012 5:43 PM

Check that there isn't another load on the 12 volt battery that has low voltage. It's not uncommon to find that a piece of 12 volt equipment has been connected to one battery. If not, just replace the the bad battery.

Register to Reply
3
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#4

Re: 12 Volt Battery Charging

08/12/2012 8:26 PM

Actually when you have a 24 volt system you have to change both batteries at the same time, a matching pair, or you will just continue to have problems being the used battery will not match the new one causing one to continually get over charged while the other stays undercharged like you have now which will quickly ruin both of them.

Being cheap will always cost you more than doing it right the first time.

Register to Reply Good Answer (Score 3)
Guru
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2011
Location: 18N 65W o
Posts: 1003
Good Answers: 28
#5

Re: 12 Volt Battery Charging

08/12/2012 9:14 PM

X2 on TCM, if you discover that one battery is bad, (sounds like 1 cell) replace both batteries.

Register to Reply
2
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#6

Re: 12 Volt Battery Charging

08/12/2012 10:42 PM

Disconnect each 12v battery from the system and each other and charge each with a 12v battery charger until each is fully charged or should have been fully charged. If available, test each battery independently with a battery load tester (this is sometimes called a "carbon pile" or other load tester) if available. If not available, test each battery with a volt meter after sitting for at least an hour.

If either battery fails replace it. If one fails and the other is of the same age or similar in age replace it too with one identical to the new battery. If the good one is new or very recent, reuse it. If there is any doubt about its condition, replace it! Reconnect the 12v batteries in series and to the starter system. You should have no problems with the battery part of the starter system.

Another question- How are the batteries recharged while they are in series? Anything other than a 24v alternator may present problems for you.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply Good Answer (Score 2)
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#7

Re: 12 Volt Battery Charging

08/12/2012 11:47 PM

The 12V battery is low. The 10V is empty. Charge the darn things individually. When unsccesful in keeping them charged, throw them out, as uncounted people before me told you. A dead battery = is a dead battery, end of discussion.

Register to Reply
Guru

Join Date: Aug 2010
Location: Melbourne, Australia
Posts: 740
Good Answers: 24
#8

Re: 12 Volt Battery Charging

08/12/2012 11:57 PM

Either the 10 Volt battery is well discharged or it has a shorted cell.

Also your 12.5V battery does not seem to be fully charged - I would expect a higher float voltage, specially if it was just disconnected from a charger or alternator.....

Register to Reply
Power-User

Join Date: Nov 2008
Posts: 116
Good Answers: 4
#9

Re: 12 Volt Battery Charging

08/13/2012 4:44 AM

Hi All, I have a similar problem with my golf buggy. 4 off 12volt batteries in series to give 48 vdc. One battery is down at 11 volts whilst three are at 13+. From what you guys are saying it will be necessary to replace all four batteries and not just the one that is low.Can one of you please be kind enough to confirm this for me as I do not want to just replace the one and find I have still got a problem.

Many thanks

Oliver Dunthorne (Hydraulic engineer "not electrical!"

Register to Reply
Commentator

Join Date: Apr 2008
Location: Rhode Island, USA
Posts: 56
Good Answers: 5
#12
In reply to #9

Re: 12 Volt Battery Charging

08/13/2012 9:49 AM

This is a fairly common problem with golf carts. They usually run the lights off from one of the 12 volt batteries. That battery doesn't get fully charged , as the charging is from a 48 volt charger. They get away with that because the lights are infrequently used on a golf course. The problem surfaces in golf cart communities where the carts are often used at night. The best solution is to buy and install a 48 to 12 volt converter for the lights.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#10

Re: 12 Volt Battery Charging

08/13/2012 5:03 AM

The main reason for such problems (assuming for the moment that both batteries are the same age type and make) is a badly designed/cheapo charger.

Where more than one 12 volt battery is in use, its actually best to use a separate 12 volt charger for each battery. A charger that does not float or over charge. One that does not gas or overheat the batteries.....

Another good trick is to buy larger batteries than you need, say for example 50% larger and to only charge them to around 70% of capacity (to around 13.2 volts only), then stop charging. Restart charging when the get down to 12.6 volts.

They will never gas, get hot and they will last years and years......

Used SLA versions if in an enclosed area, even though gassing should never happen as any battery gas is explosive. Follow the laws for where you live.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2012
Posts: 595
#11

Re: 12 Volt Battery Charging

08/13/2012 6:09 AM

not exactly to the topic Additives to Boost Flooded Lead Acid

(if the 10V one is OK has lowwer internal resistance ... blah blah blah ...)

__________________
ci139
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#13

Re: 12 Volt Battery Charging

08/13/2012 11:44 AM

26 VDC voltage from a no load battery charger is a little low. If that is how you took the voltage. And yes starting the generator from the charger may cause it harm. Unless you have one that has a motor starting function.

About replacing batteries in series it is aways a good idea to replace both when one goes bad. As batteries age the internal resistance in the cells change. The lead plates break down, lose surface area which increase resistance. This some time causes one battery or batteries depended upon how many connected in series to over charge. The new one being under charged. This lead to a circle of replacing a battery periodically and not getting the full life from them.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Power-User

Join Date: Oct 2007
Location: S. California, USA
Posts: 279
Good Answers: 12
#14

Re: 12 Volt Battery Charging

08/13/2012 12:11 PM

Of course it is easiest to just replace the batteries, but that may not be necessary. When the battery companies came out with the no maintenance battery, The art of maintaining the lead acid battery faded away. A no maintenance battery just has cell caps which are more difficult to open. Check the electrolyte in each cell. Use distilled water to top off the cells to the indicator. Do not overfill.

After the battery is charged you can use a Hydrometer to check the charge of each cell. And here is a trick: Without access to the terminals to the individual cells you can still measure the voltage of each cell. The voltage of the center cells are measured, with the cell caps off, by simply touching the volt meter probes to the electrolyte of adjacent cells.

Rule of thumb: Old battery below 9.6v for more than a day will not be recoverable. Below 12.0v and above 9.6v indicates a discharge that can probably be recovered.

Register to Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#15
In reply to #14

Re: 12 Volt Battery Charging

08/13/2012 2:23 PM

From the original post:

"If we continue this method any problem will be created to battery charger or to the good conditional battery ?"

OP realizes one battery is bad. He is asking about the consequence of leaving it in place and continuing operation.

The consequence of this choice will be system failure. The resolution, as has been said, is to replace defective components before failure.

__________________
Semper Ubi Sub Ubi
Register to Reply
Power-User

Join Date: Oct 2007
Location: S. California, USA
Posts: 279
Good Answers: 12
#18
In reply to #15

Re: 12 Volt Battery Charging

08/13/2012 3:42 PM

Agreed - I was offering a third option because the OP is apparently reluctant to spend the money for new batteries.

Option 1: Keep using with 12.5V & 10V batteries. Risk of system not performing intended purpose & risk of damaging charger. Lowest initial cost, but potentially the highest cost if system or charger are damaged.

Option 2: Replace batteries. Lowest technical risk. High cost.

Option 3: Restore operation of low battery. Low technical risk. Low cost.

Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#19
In reply to #18

Re: 12 Volt Battery Charging

08/13/2012 3:56 PM

Okay, Snave, I'm with ya. However, from the OP: "In my ship to start one generator we are using 2 no of 12 volt batteries..." A ship? Sea vessel? Sorry, I believe this is a poor place to economize on batteries.

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#17
In reply to #14

Re: 12 Volt Battery Charging

08/13/2012 3:29 PM

GA

Makes sense...

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Oct 2010
Location: OZ, otherwise known as Oklahoma were the wind comes sweeping down the plains.
Posts: 159
Good Answers: 4
#16

Re: 12 Volt Battery Charging

08/13/2012 2:59 PM

Try swapping the position of the two batteries, if the low voltage follows the battery, then you likely have a bad battery. If the low voltage does not follow the battery, you have a problem with your charging system or there is a drain on the low battery.

Register to Reply
Register to Reply 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (2); ci139 (1); DaveR (2); Doorman (3); Grand Poobah (1); JWthetech (1); leveles (1); lyn (1); old salt (1); Oliver Dunthorne (1); ozzb (1); Snave (2); tcmtech (1); WAWAUS (1)

Previous in Forum: Class 0.3 CT for Revenue Metering   Next in Forum: Regarding Generator VAR Capability

Advertisement