Absolute XMTR Using for Styrene Recovery

08/12/2012 2:49 PM

using rosemount 3051TA model sensor range is 0-2.1kg/cm2 -a , & calibration use for 0-100mmHG Fieldbus

scale is always go for 100% mean always read 101mmhg where in parallel installed same model same range another three are xmtr read 80, some 60, this one is in middle read 101mmHG installation is like xmtr is above 1.5mtr height than capillary pad,

quastion is first how to calibrate absolute xmtr & does hight of capillary pad will taken in count of we calibrate this?

what we did is here,

we deplug xmtr @ atmosphere and read 748mm at DCS and then applied vaccume 100mmhg by druck 610 but i read's 657 mmhg so now next is confuse what do or how to do..?

we are confused about calibration for this & how to set XDscale for this? where should we set zero & then get 100mmHG span ..if somebody would like to look in this and provide detail info it will be greatfull forever.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: absolute xmtr using for styrene recovery

08/12/2012 2:58 PM

What does your process engineer say? What does your instrumentation engineer say? What does the owner's manual say? What does Rosemount say?

Have you tried any of those?

Reply Off Topic (Score 5)
Anonymous Poster #1
#2
In reply to #1

Re: absolute xmtr using for styrene recovery

08/12/2012 3:57 PM

range is 0-100mmhg, it should comply with another 3 xmtr reading like 80to 60 in mmhg but it's not so we need to calibrate it

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Absolute XMTR Using for Styrene Recovery

08/13/2012 3:49 AM
  • There are two pressure gauges on a vessel showing different readings. Which one does one believe <rhetorical question - NNTR>?
  • Has this plant been the subject of a HazOp Study?

Have the instruments recalibrated off-line by qualified instrumentation technicians. Rationalise the instrumentation installed so that only one set of readings is obtained, and go forward from there.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#4

Re: Absolute XMTR Using for Styrene Recovery

08/14/2012 2:21 PM

I'm stuck on a couple issues. 1 - I haven't used Foundation Fieldbus so I don't understand how it displays locally vs on the DCS; 2 - I don't know what a 'capillary pad' is or how it uses or connects to the transmitter.

It is my understanding that the value the transmitter measures is available to the DCS, the range is only established for display purposes. The measurement is not limited, like a 4-20mA is limited, the measurement covers the entire the span of the instrument. So, it isn't clear to me, what a 'range of 100mmHg' really means.

Some issues in general with absolute pressure measurements:

1) When an absolute pressure transmitter is open to the atmosphere,
it measures barometric pressure. The "standard" for sea level is 760mmHg A, but even a sea level measurment varies with the local weather. Elevation above or below seal level is evident in the measurement.

When you "deplug xmtr @ atmosphere and read 748mm at DCS" that's normal and typical of what it would read. It shows you're a little above sea level.

A reading this close to atmospheric barometric pressure indicates to me that the pressure transmitter is working properly.

2) Error:
The Druck 610 is an Intrinsically Safe portable pressure calibrator.
If it applies -100mmHg (gauge, with respect to atmosphere), then the 3051 TA should read

748mMHg A minus 100mmHG g = 648 mmHg

When the transmitter reads 657 mmHg A, there is an error of 9 mmHg

3) Mounting position (whether the transmitter is upright or on its side or at some angle from the vertical)
Mounting Position Effects, per Rosemount's spec:
"3051T Zero shifts up to 2.5 inH2O (6.22 mbar) (4.67mmHg), which can be calibrated out. No span effect."

If "calibrated out", then all measurements must be made with the transmitter in the same mounting attitude (like zero check at atmosphere).

The 4.7mmHg of mounting error could be a potential error contribution.

4) It isn't clear exactly what the transmitter reads in-situ, in its installed location.
If the reading is 100mmHg A, give or take, then one thing to look for is leaks. It doesn't take much of a leak to suck in atmosphere and get from 80 mmHg A to 100 mmHg A

5) Foundation Fieldbus has a bunch of function blocks, some of which that can be used to jigger the output value. Have you checked through the FB settings?

Reply
Anonymous Poster #1
#5
In reply to #4

Re: Absolute XMTR Using for Styrene Recovery

08/18/2012 12:24 PM

your issue no1-in FF ( fieldbus foundation) generaly use XD scale for output scale suppose your xmtr calibrated 0-100 mmhg & if you want use 25-75mmhg you no need to re-calibrated at set everything , just apply figure in XD scale output scale 0%=25mmhg & 100% =75mmhg so what you want it done by XD scale, now if incase if Process value will go below 25mmHg like 24,,,20,,15,,,1mmhg you can read at DCS same figure but it will come as alarm ,so means your 0-100mmHg you scale will give you reading this is speciality of XD but out of XD PV will in alarm condition,

your issue2-capillary pad means simple , capillary tube attach diagphram type xmtr,

would you like to give guidance how to calibrate Absolute xmtr for 0-100mmhg & specially if calibration range is 0-2 kg/cm2 ( absoute) ?............

it will greatfull

Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#6

Re: Absolute XMTR Using for Styrene Recovery

08/19/2012 1:26 PM

Which brand and model absolute transmitter?

What is the link to the FF version manual for the transmitter?

Is this what you call a capillary pad?

How close is the absolute reading to local barometric pressure when your seal's diaphragm is at atmospheric pressure? How much error is there?