Rccb Tripping During Supply Exchange

08/15/2012 9:51 AM

Hi

RCCB is tripping whenever there is exchange of power supply from the utility to generator. There is no fault in the circuit, what might be the cause?

Regards

Mtonyole

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#1

Re: RCCB TRIPPING DURING SUPPLY EXCHANGE

08/15/2012 10:09 AM

The RCD will trip if there is an inbalance between what goes out and what comes back. If one of your breakers has a slight delay on the neutral pole when switching you could easily trip the RCD.

Register to Reply Good Answer (Score 2)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2
In reply to #1

Re: RCCB TRIPPING DURING SUPPLY EXCHANGE

08/15/2012 5:18 PM

Neutral??? An RCD uses a CBCT, so all 3 phases and the neutral will pass through it. The RCD therefore will trip ONLY for an earth leakage. No unbalance in phases or neutral should actuate it.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#3

Re: Rccb Tripping During Supply Exchange

08/15/2012 11:20 PM

check neutral/earth on both sources.

__________________
pnaban
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#4

Re: Rccb Tripping During Supply Exchange

08/16/2012 1:58 PM

You might have a neutral wire wounded and making a slight contact with a grounded chassis or frame, somewhere in the circuitry.

If the neutral to ground on the generator is very good an near enough, and the neutral of the generator is being switched On and OFF with the change/Over, then the leak will be a little bit greater than when on the Utility supply ( maybe??).

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#5

Re: Rccb Tripping During Supply Exchange

08/17/2012 3:28 AM

Another thought - when you disconnect the supply from the land supply to the generator are all connections broken. If there is disturbance on the line and lets say a voltage between neutral and earth has been caused this could be seen by the RCD as an imbalance and cause the trip.

Is the RCD there for personnel protection or because you have issues with a high Ze.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6

Re: Rccb Tripping During Supply Exchange

08/20/2012 11:52 AM

Possible harmonics, amplified by the greater generator impedance?

Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); kvsridhar (1); LAA_Lucke (1); pnaban (1); silverfox (2)

Previous in Forum: Security Lighting System Fault Tracing   Next in Forum: Component Search

Advertisement