(3pole + N) vs 4pole Breaker

08/22/2012 4:46 AM

Hi Everyone!

What is the application of (3pole + N) vs 4pole breaker for three phase and

(1pole + N) vs 2pole breaker for single phase. Thanks.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Anonymous Poster #1
#1

Re: (3pole + N) vs 4pole breaker

08/22/2012 5:04 AM
Register to Reply
Commentator

Join Date: Sep 2009
Location: Singapore
Posts: 77
Good Answers: 1
#2

Re: (3pole + N) vs 4pole breaker

08/22/2012 5:24 AM

I am reffering for the load side. I've seen welding outlet that using 4pole breaker while package motor is using 3pole+N . Both of them are using 4core means they have neutral. The voltage is 415V. Note (3P+N) means 3pole is overcurrent while N is just a switch connected in the breaker.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: (3pole + N) vs 4pole breaker

08/22/2012 6:03 AM

Follow the electrical codes applicable in the country of installation. In the UK, for example, it would be British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: (3pole + N) vs 4pole breaker

08/22/2012 8:44 AM

Ask the Client.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: (3pole + N) vs 4pole Breaker

08/22/2012 9:56 AM

In TPN (three pole + neutral) breakers, only three phase poles would have the releases (thermal & magnetic) and the fourth neutral pole is only a switch without any releases in it. Whereas in four pole breakers, all the four poles would have releases.

Same is the case with SPN & DP breakers.

Hope it is clear.

Register to Reply Good Answer (Score 2)
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#6

Re: (3pole + N) vs 4pole Breaker

08/22/2012 12:21 PM

3p + n would be for a nice clean known load. If you are specifying a 4 pole breaker it may because you have have issues with harmonics and that the current in the neutral can be higher than the phase conductors. (Schneider do a good paper on a transformer with this issue.)

Years ago neutrals used to be dead but with the rubbish thats on them now it pays to treat them as live conductors with respect to earth.

2 pole MCBs are usual on a tool transformer where you have 55 -0- 55V. Although its known as a 110V supply both poles are live with respect to earth.

Neutrals are often solid because of the problems that might occur if you broke it before the phases on a TP&N distribution board say feeding lots of lights.

This said it is far from an exact science.

Register to Reply
Power-User
Engineering Fields - Piping Design Engineering - New Member Technical Fields - Architecture - New Member

Join Date: Apr 2006
Location: Bangalore India
Posts: 288
Good Answers: 3
#7

Re: (3pole + N) vs 4pole Breaker

08/22/2012 11:10 PM

to find an answer to your problem first you should understand Star and delts circutes and three phase circutes!

__________________
Run silent run deep
Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#8

Re: (3pole + N) vs 4pole Breaker

08/23/2012 10:18 AM

System deigner selects the same.

Normally, Neutral is not allowed to break in any conditions, ( except special applications)

for human & equipment safety. So, for single incomer power fed systems, 3P+N breaker is used, where, only phases are isolated during breaking operations.

But, in multi incomer power fed systems, you need not to mix up the neutrals of incoming powers, where, you can use 4P breakers, to isolate the other power sources neutrals from the incomer power neutral in use.

__________________
Exploring the Science of Electricity
Register to Reply
Register to Reply 8 comments