VFD Problem

08/22/2012 11:20 AM

Sir,

We are using ALTIVAR21 VFD in our plant. We have faced the problem in the VFD.

In the panel motor start time VFD shows "OP 1" Error and tripped the motor.

We have changed the motor and same problem exist. Kindly suggest the possibility solution to solve the issue

VFD details:

Make: Schneider Electric

Telemecanique

Model: ATV21HD45N4

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Anonymous Poster #2
#1

Re: VFD Problem

08/22/2012 11:47 AM
Reply Off Topic (Score 5)
Associate

Join Date: Mar 2011
Posts: 48
#2

Re: VFD Problem

08/22/2012 12:01 PM

please open user manual and find out "OP 1" error means what?

then its easy to other to determine what are the possibilities to generate that error

Reply
2
Guru

Join Date: Jun 2010
Location: New York
Posts: 972
Good Answers: 23
#3

Re: VFD Problem

08/22/2012 2:57 PM

BOOM pdf.

According to page 37 of said pdf, error code OP1 means you have a problem with overvoltage during acceleration. I can't even begin to tell you how to fix it, but it might be in that pdf! Or maybe with the vendor if you want to ring them up!

Good luck!

__________________
The first law of thermodynamics is you do NOT talk about thermodynamics.
Reply Good Answer (Score 2)
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: VFD Problem

08/22/2012 9:39 PM

Over Voltage during acceleration means that you a) have an over voltage condition at the line terminals, or b) your load is mechanically accelerating faster than the VFD is telling it to and the motor is becoming a generator. It would have nothing to do with the motor, don't waste more time replacing or troubleshooting it there. This is either a voltage problem or an application problem.

We don't know what this is attached to, nor do we know what your voltage is, so we can't help any more than that.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 2)
Anonymous Poster #3
#5

Re: VFD Problem

08/23/2012 11:46 PM

Regarding OP1 error that is over voltage acceleration

Reply
Anonymous Poster #4
#6
In reply to #5

Re: VFD Problem

08/24/2012 12:34 PM

Replying to Comment by Anonymous Poster #3:

Regarding OP1 error that is over voltage acceleration

A true Master of the Obvious...

Reply Off Topic (Score 5)
Associate

Join Date: Feb 2012
Posts: 25
#7

Re: VFD Problem

08/27/2012 6:55 PM

Hi,

This fault is triggered by an overvolatge condiotion at the DC bus. Possible causes

The input voltage is fluctauting abnormally. Remedy: install a line reactor.

Power factor capacitor switching. Remedy: Set F302 to 2.

Drive is starting into a rotating load. enable catch on the fly parameter : F301. I would check if any of the dampers is jammed thus causing the load to rotate before starting.

Intermittent ouptput phase fault.Since you have changed the motor but the fault exists, then we can rule out output phase loss fault assuming the motor cables have been checked.

If the unit has been running for a while and this fault just came in, then I would suggest you check VFD for possible GND faults . Yo can do this by disabling phase loss fault and running the VFD with Motor disconnected. If the VFD trips on the same fault then it likely a GND fault is causing the VFD to trip. I would also try to swap the VFD with a simimalr unit and see if the fault disappers.

If none of the above works then I would suggest you contact your nearest Schneider service center.

You can email me direct if you need further help

cheers

Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#8

Re: VFD Problem

08/12/2016 12:58 PM

Dear Friend,

Your data is not sufficient enough. You have not stated whether the motor has to start against the load or the motor is loaded after starting. If the motor is started against the load, then the Torque Demand, Gd^2 value comes in to picture.

What is OP1 - perhaps manufacturer's nomenclature/title for a specific function.

You may contact the supplier and take his help.

But I want to say the following.

1.The vfd has low starting torque, and the torque requirement may be more.

2.The voltage available at the starting moment, may be or can be in-sufficient. This is derived since the 2nd motor also does not start.

3. The driven equipment may have very high Gd^2 value and motor cannot handle thie required Gd^2. Hence the motor cannot start. This is also derived since the 2nd motor also does not start.

4. Your data, as I mentioned is not sufficient enough. You have not stated whether the motor has to start against the load or the motor is loaded after starting. If the motor is started against the load, then the Torque Demand, Gd^2 value comes in to picture.

Pl. post the information - what was the problem and how it is overcome.

DHAYANANDHAN.S

Reply
Reply to Forum Thread 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); dhayanandhan (1); JRaef (1); loyd (1); Mizuti (1); rodeh (1)