Voltage/Frequency Supply Conversion for Barge

08/26/2012 6:03 AM

Hi Guys, I just need your expert suggestion on this subject. I need to supply power 440V, 3 Phase, 60 Hz, 1600 kVA to a distribution board located on a barge which is stationed adjacent to an existing offshore platform. The available source power from the offshore platform which can be supplied to the barge (@300m away along the bridge) is 6.6 kV, 3 phase, 50 Hz. Since nearby power supply is available, please note that the barge generators will be run only in emergency situation to economize on diesel fuel in the long run.

Please advise what will be the best option to convert the voltage/frequency on the barge, whether to use a stepdown transformer with frequency converter, or cycloconverter or any other arrangement.

Thanks in advance for your valued suggestion.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Voltage/Frequency supply conversion for barge

08/26/2012 9:34 AM
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2
In reply to #1

Re: Voltage/Frequency supply conversion for barge

08/26/2012 5:36 PM

That's one hell of a MG set at 1600KVA

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: Voltage/Frequency supply conversion for barge

08/26/2012 11:36 PM

1600kVA is going to be one helluva whatever is used...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#5
In reply to #1

Re: Voltage/Frequency supply conversion for barge

08/27/2012 12:35 AM

You got there first- I have been busy tonight but THAT is exactly where my mind went.

The only other "practical"- using the term loosely- would be a UPS system but I think the MG will be cheaper AND more reliable (unless you REALLY go for "broke" and use a parrallel-redundant version where it is STILL cheaper).

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#4

Re: Voltage/Frequency Supply Conversion for Barge

08/27/2012 12:31 AM

So what part of the systems are frequency sensitive and what would the costs be to refit those parts to dual frequency capability?

Or more importantly how can you run a barge that big hauling off shore cargo and not be able to afford the fuel to run the equipment? Something is not adding up here in my views.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6

Re: Voltage/Frequency Supply Conversion for Barge

08/27/2012 1:10 AM

Are you sure about the 1600kVA figure (1.6MVA, 500 houses worth)?

What is the capacity of the shore power transformer?

Getting your voltage down is a transformer application.....straight forward enough.

Frequency conversion at the capacity you have quoted is a bit of a tall ask. At 440V no less. That solution will not be off the shelf or in a brochure. I suppose you could have lots of smaller MGs or VFDs or Rectifier/invertors other (are there any?) cycloconvertors......

Echo what TonyS and JRaef said.

What is on this barge? What types of electrical loads? Are they frequency intolerant?

What's it worth?

You will only save if

the metered cost plus the capital depreciation/lease costs plus installation costs plus removal costs plus disposal costs

is less than

the cost of the diesel(delivered) plus generator maintenance plus generator depreciation costs

If your genset is up to the job I'd be using that. But then, I'm not there so I could be second guessing badly.

What power redundancy do you have?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 21
#11
In reply to #6

Re: Voltage/Frequency Supply Conversion for Barge

08/28/2012 12:50 AM

Thanks for all your valued replies.

Wal I would like to give you the full picture. In fact there are 4 generators (1800 kVA each) feeding a 690V, 60 Hz switchboard which is further stepped down to 440V, 60 Hz and this barge will be stationed for around 2 years in one location

The generators are supposed to run intermittently only to supply the 690V loads i.e. the cranes. The external shore supply is only to the 440V distribution board which feeds all the barge utilities i.e. HVAC, lighting, UPS, RO plant etc.

Do you think using a step down trafo 6.6kV/440V, 50 Hz with a cycloconverter to 60 Hz @ 1600 kVA is practical. Is frequency conversion at such high rating feasible.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#12
In reply to #11

Re: Voltage/Frequency Supply Conversion for Barge

08/28/2012 4:16 AM

See #9.

If you run your cranes on genset only then that leaves only the barge utilities to run on shore power. Some of these loads couldn't care less what the line frequency is. Those that do could be powered through a VFD on an as needs basis.

How much time do you have to get this all working?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#7

Re: Voltage/Frequency Supply Conversion for Barge

08/27/2012 1:30 AM

Just figured it out- It is the new WikiLeaks Data Center, complete with satellite uplinks, microwave transmitters.an one helluva security system.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#8
In reply to #7

Re: Voltage/Frequency Supply Conversion for Barge

08/27/2012 1:40 AM

1.6MVA?

Satellite up links on a barge?....what the heck, those tracking drive motors would be busy is all. Microwave links with tracking too....this is one hell of a pimped barge!

Must be something else.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#9

Re: Voltage/Frequency Supply Conversion for Barge

08/27/2012 2:51 AM

Thycon in Oz make what you're after it seems. Static frequency convertor be the name of that beast.

The SFX1600 will do it. Specs on page 142.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#10
In reply to #9

Re: Voltage/Frequency Supply Conversion for Barge

08/27/2012 11:49 AM

That, and a 1.6 MVA transformer on the input side to go from 6.6kV to 415V, then another 1.6 MVA transformer on the output side to go from 415 up to 440V. Although I'm sure that for the right coin, they may be willing to make one for 440V output, so you would only need the one transformer on the input side to go 6.6kV to 440V. So by the time you are done with that static converter, the transformer and switchgear for it, plus air conditioning and safety, figure on an E-House about 40ft long, the size of a large shipping container. Doable, but not cheap and not small. I'd estimate just under $1million US.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**