Rolling of 600MW Steam Turbine

09/02/2012 6:53 AM

In a large steam turbine of about 600 MW how rolling of turbine is done?? In our case of 135 MW turbine we do HP. rolling aftr building parameters of HP turbine thts 50TPH steam flow;8~10 kg MS pressure;350deg MS temp. kindly reply with ur thoughts...

__________________
"No matter how hard the past,you can always begin again."
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: Rolling of 600MW Steam Turbine

09/02/2012 11:43 AM
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Rolling of 600MW Steam Turbine

09/03/2012 3:58 AM

Did the company that created and installed the thing produce a User Manual for it? What does it say?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Associate

Join Date: Sep 2012
Posts: 33
Good Answers: 1
#3
In reply to #2

Re: Rolling of 600MW Steam Turbine

09/03/2012 1:03 PM

The user manual mentions about initial IP turbine rolling...but why cant we do the usual HP turbine rolling??

__________________
"No matter how hard the past,you can always begin again."
Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#4
In reply to #3

Re: Rolling of 600MW Steam Turbine

09/03/2012 2:11 PM

"The user manual mentions about initial IP turbine rolling..."

Because your user manual says so! You may not...

"Do the usual HP turbine rolling."

Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#5
In reply to #3

Re: Rolling of 600MW Steam Turbine

09/03/2012 2:52 PM

ROLLING OF TURBINE THROUGH IPT DURING GENERATOR

DRY OUT (UNITS HAVING HP-LP BY PASS)

The turbine is required to be run at 3000 rpm on no load, for very long duration, when generator dryout operation is being carried out. Such no load operation may be required for about 30-40 hours or sometimes even more than this Working of turbine under such abnormal conditions, causes the exhaust hood temperature to rise beyond the permitted limit. In order to control the rise of exhaust hood temperature, it is recommended to roll the turbine through IP cylinder, thereby increasing steam flow through IP & LP cylinders The HP cylinder is kept under vacuum under such operation. By adopting this method of rolling the turbine from cold state for generator dryout it has been foreseen that the exhaust hood temperature can be kept within the permitted limit.

These instructions are valid only for the units which have HP/LP bypass stations. Prior to steam rolling the unit. relevant protections and interlocks should be got checked. The other systems like oil system. Condensate system vacuum system etc. should be put into service as per the normal procedure given in operation manual.

For starting the turbine from the cold state, the following instructions to be followed:

1. Close tightly the bypass valves of NRV in the cold reheat line, so as to stop the entry of the steam in the HP cylinder when HP bypass station is put into operation.

2. Open both the HP cylinder evacuation valves, so that the HP cylinder is kept under vacuum throughout the running of the set.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Sep 2012
Posts: 33
Good Answers: 1
#6
In reply to #5

Re: Rolling of 600MW Steam Turbine

09/03/2012 9:39 PM

This has relevantly answrd all. my queries..thank you so much sir.

__________________
"No matter how hard the past,you can always begin again."
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Joshi (3); PWSlack (1); vir540 (2)