When testing the 138kv HLR breaker with BLG mechanism with the full rated control DC power supply 130VDC the trip time 32millisecond it is good the spec is 34millisec. +/- 4 milliseconds.
According to the IEEE guideline, the breaker tested with 70VDC the breaker didn't trip. Tested with 75VDC the trip took 70 milliseconds, out of the spec. range.
Now is it a coil problem or the mechanical lubrication problem? Any one has this experience before
thanks