HLR Breaker with BLG Mechanism Trip Delay

09/02/2012 12:18 PM

When testing the 138kv HLR breaker with BLG mechanism with the full rated control DC power supply 130VDC the trip time 32millisecond it is good the spec is 34millisec. +/- 4 milliseconds.

According to the IEEE guideline, the breaker tested with 70VDC the breaker didn't trip. Tested with 75VDC the trip took 70 milliseconds, out of the spec. range.

Now is it a coil problem or the mechanical lubrication problem? Any one has this experience before

thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: May 2011
Posts: 84
Good Answers: 1
#1

Re: HLR Breaker with BLG Mechanism Trip Delay

09/02/2012 11:35 PM

90% is a coil problem.

Coil is not operating the plunger at 70 Volt DC.

Coil shoukl have a lower resistance to offer more current at 70 V DC.

Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#2

Re: HLR Breaker with BLG Mechanism Trip Delay

09/05/2012 4:27 AM

Most likely, it is mechanical friction problem. Only good remedy is replacement.