Separate Transformer in Lighting Panel?
09/02/2012 12:23 PM
why ve are using separate transformer in ligthting distribution panels.....???
I ve laid power cable from PCC to MDB... but inside the MDB thre is separate transformer... both the primary/secondary rating are in 415v... then why ve are using separate transformer....
Good Answers: 34
Re: Separate Transformer in Lighting Panel?
09/02/2012 4:47 PM
Is secondary, connected to all the load distribution points? It will provide isolation from grid, since isolated from grid ground/neutral. Shock hazard will be eliminated. Generally used in hospital equipments wired to patients & service bench,
Good Answers: 170
09/03/2012 9:15 AM
Good observation!
This is to reduce the fault level of the lighting circuit. Normally, one would use a very small cross section (of say, around 2.5 sq.mm Copper) for lighting circuits. If a transformer is not used, then, if there is a short circuit at a lighting point, the short circuit current supplied by a larger power transformer would not be tolerated by the small lighting wire and it would damage, even causing fire accidents. A suitably rated lighting trafo would reduce this fault level within the tolerance limits of the wire.
Other reasons could be better voltage regulation, isolation, etc.
09/03/2012 12:52 PM
Thnks for ur reply Mr.Electrical expert please elobarate me more sir...... iam not getting clearly the point......