Protection of Metering CT

09/05/2012 6:40 AM

when severe fault curtrent will pass through metering CT it may damage the metering instrument or may saturate the CT . What are the protective action we are taking against this?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: protection of metering CT

09/05/2012 6:45 AM

It won't. It can't - the overcurrent device in the primary will operate first.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Commentator

Join Date: May 2011
Posts: 84
Good Answers: 1
#2

Re: protection of metering CT

09/05/2012 8:34 AM

knee point voltage is low in metering CTs so that they saturate during fault currents. Thus metering instruments are saved from these fault currents due to saturation.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Protection of Metering CT

09/05/2012 9:59 AM

...and during a fault event, the important thing is to trip the overcurrent device at the earliest mossible moment. If this action should also turn off the metering, so what <rhetorical question - NNTR>?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Protection of Metering CT

09/05/2012 10:42 AM

Go for a metering CT with a low ISF (Instrument Security Factor). This will save your meters from receving a high reflected fault current. The minimum ISF possible for metering CT is 2.

Register to Reply Good Answer (Score 2)
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#8
In reply to #4

Re: Protection of Metering CT

09/20/2012 6:32 AM

Can you elaborate this sir???

__________________
"Know something about everything and everything about something"
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#5

Re: Protection of Metering CT

09/06/2012 12:42 AM

The knee-point voltage is less applicable for metering current transformers. The concept of knee point voltage is very pertinent to protection current transformers, as they are exposed to very high fault currents. Since accurate meters are very sensitive to over currents, we do not want that a high fault current to pass through the meters, otherwise they will get damaged. We want the CT to saturate at high current so that the meter is safe.

Accuracy classes for CTs for various types of measurement are specified in IEC 60044-1 as Classes 0.1, 0.2, 0.5, 1 and 3. The class designation is an approximate measure of the CT's accuracy. The ratio (primary to secondary current) error of a Class 1 CT is 1% at rated current. If we try to measure 100A with a class 1 CT, the measured value may be either 101 A or 99 A or anything in between these range

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#6

Re: Protection of Metering CT

09/06/2012 1:22 AM

So as you heard after installation of the TC and metering you can't take protective actions.

The best thing you can do is to choose wisely the instrumentation in the first place. The meters have maximum current of 10 or 20 times (maybe even more) the rated current so you can see the protection is built in itself.

PS: I will assume that you know the maximum short circuit current in your installation and that you chose the CTs and metering accordingly.

__________________
The time is ......now
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#7

Re: Protection of Metering CT

09/06/2012 3:21 AM

don't put any protection in a CT circuit. If you take the load off the CT it will generate very high and dangerous voltages which can in turn blow the CT.

Register to Reply Score 1 for Good Answer
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

debata07 (1); electricalexpert65 (1); giri (1); muditmah (1); nikolay (1); PWSlack (2); silverfox (1)

Previous in Forum: Clearance Required For Erection of 132 KV Transmission Line   Next in Forum: Holm's or Blow-Off Force Calculation

Advertisement