Anonymous Poster #1

Control Valve Troubleshooting or Testing

09/05/2012 10:54 AM

Dear CR4 members

Recently I am employed as instrumentation tech. In this factory, there are numbers of valves and positioners disassembled from each other and stored in the warehouse. The maintenance manager is concerned about storage space limitation and gave the work order to trash them or repair them.

My experience from electric motor repair show that I can rotate/move the shaft of whatever mechanism drove by electric motor. If I cannot move it, I can say the driven mechanism or the motor is bad. On the same way, I tried to rotate the shaft (moving part) of the valves by hand then by lever (adjustable wrench) but I can´t move (rotate) any of the valves. Hence:

1) If I could not move the shaft of the valves by hand how the positioner (actuator) or the control drive can move the shaft of the heavy valve?

2) What are the criteria to say the valve shaft is not moving, bad or stack?

Your help will be appreciated

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Control Valve Troubleshooting or testing

09/05/2012 10:57 AM

A1) It can't.

A2) It cannot be moved by hand.

Q3) Why is this facility storing junk instead of weighing it in?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster #1
#2
In reply to #1

Re: Control Valve Troubleshooting or testing

09/05/2012 11:22 AM

Thank you for your replay. Still I am not sure.

What is the procedure to say the valve is mechanically bad or good? How you test the valve`s shaft motion or rotation? Let consider the valve is already in production line. How you decide specifically the valve is bad? On another saying, how you identify the actuator (positioner) is good but the valve is bad? Please comment more if you have detail experience in this area.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #2

Re: Control Valve Troubleshooting or testing

09/05/2012 11:39 AM

Q4) Does this facility have a Planned Preventative Maintenance programme?

Q5) What information is derived from Quality Management initiatives?

Q6) Where are the bottlenecks in the production facility?

Q7) If there are so many dud parts on the shelf, what are the Instrumentation Technicians actually doing?

Q8) If there is a need to ask a global engineering forum how to service a valve and a positioner, how did the Instrumentation Technicians get their jobs and how do they keep their jobs?

Q9) Why is the training programme for Instrumentation Technicians ineffective?

Q10) If the facility has hired so many non-productive Instrument Technicians, how does their supervisor keep in a job?

Q11) What is the facility's procedure for writing-off dud assets from its books, and why is the procedure not being followed?

Q12) What is the facility's record in regard to loss prevention and product re-work?

Q13) What is the facility's record with regard to heaalth and safety?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 2 for Off Topic
Anonymous Poster #1
#5
In reply to #4

Re: Control Valve Troubleshooting or testing

09/05/2012 12:30 PM

Hi again,

When I wrote this post I already announced that I have lack of experience in this specific area.

I guess, the objective of CR4 is cooperation on positive idea. Negative ideas or questions are not helpful as do positive ideas. I appreciate if you answer the key question to the point. Big job is undone due to lack of a key idea. I am looking for that key idea from this CR4.

I guess, when you are not answering to the point that tells me we are at the same experience level. That is normal, our experience depend from our exposure. So it is better to wait for CR4 members who have experience and willingness to share knowledge. I believe that there are numbers of CR4 members who are volunteers to help others.

Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7
In reply to #5

Re: Control Valve Troubleshooting or testing

09/05/2012 12:49 PM

Not all valves are the same. The manufacturer is the only one who can tell you what the acceptance criteria will be.

Do as any good engineer would do. Contact the valve maker and ask them to educate you.

Reply Score 1 for Off Topic
Associate

Join Date: Apr 2012
Posts: 42
Good Answers: 1
#12
In reply to #4

Re: Control Valve Troubleshooting or testing

09/06/2012 12:12 AM

rather dickish, don't you think?

Reply Off Topic (Score 6)
Associate

Join Date: Apr 2012
Posts: 42
Good Answers: 1
#13
In reply to #12

Re: Control Valve Troubleshooting or testing

09/06/2012 12:22 AM

wtf? nice little diatribe - got issues?

Reply Off Topic (Score 6)
Associate

Join Date: Apr 2012
Posts: 42
Good Answers: 1
#15
In reply to #13

Re: Control Valve Troubleshooting or testing

09/06/2012 12:44 AM

No really, you got issues & need help if you can't control yourself & feel free to rip on somebody like that. Get help.

Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Control Valve Troubleshooting or testing

09/05/2012 11:34 AM

Take the valves apart and look at them. You need the experience.

If after re-assembling the valve won't move, trash it.

You should know how to test the actuators.

Please share with us how one goes about getting a job for which one is not qualified.

Reply Score 1 for Good Answer
Anonymous Poster #1
#6
In reply to #3

Re: Control Valve Troubleshooting or testing

09/05/2012 12:43 PM

Hi,

Thank you for your comment;

Can you list few items about what to look on disassembly/assembly? What are common issue regarding to hard to rotate the Valve´s shaft? Can I try to drive by using cordless power drive machine (tool)?

Thank you

Reply
Anonymous Poster #2
#19
In reply to #3

Re: Control Valve Troubleshooting or testing

09/06/2012 2:33 AM

CR4 ADMIN: Deleted Post

Vulgar/Rude/Improper Behavior: This post was deleted because it did not adhere to the behavioral policies of the site. Please review Section 14 of the CR4 Site FAQ and the CR4 Rules of Conduct.

Reply Off Topic (Score 5)
Guru
United States - Member - USA! Hobbies - Musician - Sound Man Engineering Fields - Mechanical Engineering - More than a Hobby Technical Fields - Technical Writing - New Member

Join Date: Oct 2008
Location: City of Roses.
Posts: 2056
Good Answers: 101
#8

Re: Control Valve Troubleshooting or Testing

09/05/2012 4:23 PM

WHAT KIND OF VALVES?

There are numerous styles of valves/actuators.

Some rotate, some are driven by a coil/spool.

Ball valve?

Hydraulic cartridge valve?

D03, D05

Butterfly?

36" diameter, or 1/4" diameter?

Pneumatic actuation?

Etc Etc Etc.

__________________
Don't believe everything you read on the Internet!
Reply
Anonymous Poster #1
#9
In reply to #8

Re: Control Valve Troubleshooting or Testing

09/05/2012 5:49 PM

Thank you so much for your comments,

All are rotary valve: ball valves or butterfly valves. One example is "nels controls valve" type B1JU8/25. I tried to search for the manual but I could not find any.

I am looking to get general strategy to test:

1) To drive should be there a process flow through the valve?

2) Can I use more lever force or cordless power tool? I am worried in case I break some interlocking mechanism due to lack of detail.

Thanks a lot

Reply
2
Guru
United States - Member - USA! Hobbies - Musician - Sound Man Engineering Fields - Mechanical Engineering - More than a Hobby Technical Fields - Technical Writing - New Member

Join Date: Oct 2008
Location: City of Roses.
Posts: 2056
Good Answers: 101
#10
In reply to #9

Re: Control Valve Troubleshooting or Testing

09/05/2012 6:07 PM

If it's meant to turn, put enough force on it til it either turns or breaks... If it breaks, throw it away, if it turns, evaluate it further.

Meh...

__________________
Don't believe everything you read on the Internet!
Reply Good Answer (Score 2)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#11
In reply to #10

Re: Control Valve Troubleshooting or Testing

09/05/2012 7:02 PM

I expect that, using your method of testing, the OP will be able to quickly separate the "good" valves from the "bad" valves.

And if the tester (OP) is as intelligent as I think he is, he will make sure that the "bad" valve barrel is at least twice as big as the "good" valve barrel.

Reply
Anonymous Poster #2
#20
In reply to #11

Re: Control Valve Troubleshooting or Testing

09/06/2012 2:57 AM

Sight unseen. Poobah speaks, 1 good - 2 bad. Or thereabouts cuz I know. Thats that. LMAO again, LMAO still

Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#14

Re: Control Valve Troubleshooting or Testing

09/06/2012 12:31 AM

"Some will help you here. Some will not."

Will you EVER help anyone?

Or will you just bitch and whine?

Never mind, you are hopeless!

I look forward to your next exhibition of ignorance. How low will you go?

Reply Off Topic (Score 4)
Associate

Join Date: Apr 2012
Posts: 42
Good Answers: 1
#17
In reply to #14

Re: Control Valve Troubleshooting or Testing

09/06/2012 1:21 AM

CR4 ADMIN: Deleted Post

Vulgar/Rude/Improper Behavior: This post was deleted because it did not adhere to the behavioral policies of the site. Please review Section 14 of the CR4 Site FAQ and the CR4 Rules of Conduct.

Reply Off Topic (Score 5)
Anonymous Poster #2
#18
In reply to #14

Re: Control Valve Troubleshooting or Testing

09/06/2012 2:12 AM

Lyn gets another GA - yeah!!!!!!

he's special!

Reply Off Topic (Score 5)
Associate

Join Date: Apr 2012
Posts: 42
Good Answers: 1
#21
In reply to #14

Re: Control Valve Troubleshooting or Testing

09/06/2012 4:13 AM

CR4 ADMIN: Deleted Post

Vulgar/Rude/Improper Behavior: This post was deleted because it did not adhere to the behavioral policies of the site. Please review Section 14 of the CR4 Site FAQ and the CR4 Rules of Conduct.

Reply Off Topic (Score 5)
Associate

Join Date: Apr 2012
Posts: 42
Good Answers: 1
#22
In reply to #14

Re: Control Valve Troubleshooting or Testing

09/06/2012 4:20 AM

And there they are.

Reply
Associate

Join Date: Apr 2012
Posts: 42
Good Answers: 1
#16

Re: Control Valve Troubleshooting or Testing

09/06/2012 12:51 AM

Data request off topic & NFG? ok.

Reply Off Topic (Score 5)
Guru

Join Date: Jun 2011
Location: Mossel Bay, SA
Posts: 777
Good Answers: 21
#23

Re: Control Valve Troubleshooting or Testing

09/06/2012 5:32 AM

I assume these valves are quite large, so it is no surprise that you cannot rotate them by hand. That is why they have actuators, nearly all of which are designed to exert more torque than can normally be applied by hand. I doubt if your 'cordless' tool will be effective at all.

Generally, the thread on the spindle will have rusted/ corroded/ become dirty and will become difficult to turn, or the bearings/ bushes have seized and the valve requires an overhaul. The valve 'plug' itself is only something attached to the spindle.

You need to note that 'butterfly' and 'ball' valves are not designed to rotate fully in valve the body. They generally operate only over 90 deg/ quarter turn. Only 'gate' valves run in a vertical guide where you can turn the spindle continuously until closed.

Therefore, you can see actually whether the butterfly valve is worth repairing, you need to open the ball valve and check the condition of the ball and seats to make a call for scrapping, and you can see inside 'gate' valves as to whether the plug is seized up in the guides or whether it's just the spindle sticking. Where some of the valves may be 'globe' valves, I wouldn't scrap these unless the body casting is suspect.

There is no formula...except the top dog wants to get rid of some valves because the premises are resembling a scrap yard.....make him happy.

Reply Score 1 for Good Answer
Associate

Join Date: Jan 2010
Location: USA
Posts: 27
#24

Re: Control Valve Troubleshooting or Testing

09/06/2012 6:31 AM

This is something that has come about continuously over shops. Unfortunately some shops do not have a QA/QC program in place that would always require paperwork. Maybe this is something that you maybe able to bring to management's attention. Some type of traceability of paperwork usually always helps it can't hurt. To answer your question, depending on size of the valves you may be able to hold the valves stationary in a vise or a valve clamp and try opening it. Depending on how this has been stored check the seating areas to make sure debris is not in the patch of the seat if visible. Prior to trying this maybe start some type of paperwork to list all particular of valve or instrument. There are many reports that can be filled out for this, if your facility does not have one. A seat leak test and shell test can be done to see if the valve is salvageable (if valve can be functioned). This is just a start and after this a detailed report can be attached with the stored product so the next one looking at this valve will have something to go by. Make sure the product(s) are stored correctly. Tags on valves are not always what they say they are, so be careful with that as well, you must provide your customer with adequate application. If the valve has changed the tag does accommodate the properties as well. I am sure you can accomplish this with little time and patience.

__________________
always find time to do it right the first time or.............................
Reply Score 1 for Good Answer
Power-User

Join Date: Jan 2008
Location: kuwait
Posts: 132
Good Answers: 2
#25

Re: Control Valve Troubleshooting or Testing

09/09/2012 5:51 AM

kindly read carefully the valves instruction manual and find the driving force (needed to operate the valve the more force can damage the seats of it.otherwise open the valve and examine the axis of it (to find the reason for sucking)

__________________
love4everyone
Reply Score 1 for Good Answer
Reply to Forum Thread 25 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (7); drmilr (7); Hilton (1); lyn (4); PWSlack (2); RVZ717 (2); sohail0110 (1); TRICKYDIC (1)

Previous in Forum: Skin RTD   Next in Forum: Level Transmitter

Advertisement