Contactor Continuity Question

09/09/2012 12:39 PM

Hey all

I am still fresh here. I just had one 3 phase induction motor. Connected in delta. Tried to run but was making some sound but it was not spinning. I doubted the contactor for single phasing. I switced off the power and the checked continuity( by pressing the contactor) between l1 and t1 l2, t2 ,l3 t3 of the contactor .I heard the beep so I assumed it was ok but when my senior came.He checked the resistance not continity it was showing mega ohms .wth. How can multimeter beep with megaohms.

PS; relaced contactor and we had our motor running

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: Contactor continuity question

09/09/2012 1:20 PM

If what you state is correct, then what you observed, ie. (How can multimeter beep with megaohms) can not be true. You must have missed something.

Register to Reply
3
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Contactor Continuity Question

09/09/2012 3:16 PM

Continuity is a good first indicator tool but doesn't tell you the full story sometimes (sometimes the continuity setting can be fooled).

If you open up the old contactor you will probably find the contact points to be burnt causing an intermittent or poor connection, and if you retest by pressing the contactor contacts together a few times some tests may show high resistance while some tests show low resistance (intermittent contact).

__________________
jack of all trades
Register to Reply Good Answer (Score 3)
Commentator

Join Date: Aug 2010
Posts: 56
#4
In reply to #2

Re: Contactor Continuity Question

09/09/2012 8:30 PM

@jack,

you are right. I checked the contactor now. Sometimes shows high and some times low resistance,.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#6
In reply to #4

Re: Contactor Continuity Question

09/09/2012 8:37 PM

I have been there before, and it's not the sort of thing they adequately prepare you for in any education course. Somethings must be learnt the hard way - through simple trial and error.

__________________
jack of all trades
Register to Reply Off Topic (Score 4)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #4

Re: Contactor Continuity Question

09/10/2012 3:33 AM

Replace it.

Destroy the old one mechanically so that it cannot be selected for re-use.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#9
In reply to #2

Re: Contactor Continuity Question

09/10/2012 7:38 AM

In many years of repairing electromotive equipment this problem was common. I would check for a load drop across the contacts. Making and breaking them several times to see if it changed.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#3

Re: Contactor Continuity Question

09/09/2012 4:47 PM

You should not rely on the beep, but check the actual resistance.Depending on your set up the are better ways to test than pressing the contactor.

Register to Reply
Guru

Join Date: Sep 2012
Location: Iowa, USA
Posts: 577
Good Answers: 50
#5

Re: Contactor Continuity Question

09/09/2012 8:36 PM

How often does this motor run? How many watts?

Where is the location of the contactor? Protected from weather, mainly condensing humidity?

What voltage is the system?

I've seen contactors on outdoor condensing units that sit over the winter, and then the compressor does not start in the summer. They corrode and even though smooth not damaged contacts, the oxide prevents (in this case 240VAC) to break through this insulating oxide.

As another poster indicated, inspect the contacts for arching damage.

__________________
ignator -
Register to Reply
Power-User

Join Date: Jan 2010
Location: Atchison Village
Posts: 383
Good Answers: 39
#7

Re: Contactor Continuity Question

09/10/2012 2:18 AM

Teeny red ants will self-immolate, like tiny worshippers at the shrine of silver contacts. For some reason they're attracted to the contacts, usually on espresso machines. This was in Key West. Must have fixed twenty machine by simply using a matchbook cover to remove their chitinous remains.

__________________
Align culture with nature...
Register to Reply
Power-User

Join Date: Feb 2009
Posts: 176
Good Answers: 6
#10

Re: Contactor Continuity Question

09/10/2012 11:20 PM

Your continuity meter should only beep at below 100 ohms but it could be faulty so always check what the reading is on the display. Another thing I have noticed when pushing the contactor in manually you can get good readings & when the contactor is pulling in under it's own power the contacts don't make correctly if they are damaged.

Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

brettj1au (1); eltech (1); ignator (1); jack of all trades (2); Joshi (1); ormondotvos (1); ozzb (1); plckid (1); PWSlack (1)

Previous in Forum: LED Driver   Next in Forum: Passenger Elevators

Advertisement