Voltage Factor for CVT

09/15/2012 3:13 AM

The value for voltage factor depending on earth system. Why rely on determining the type of earthing sysem

Register to Reply
Pathfinder Tags: SHORT TIME V. FACTOR
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: VOLTAGE FACTOR FOR CVT

09/15/2012 9:02 AM
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Voltage Factor for CVT

09/15/2012 1:59 PM

STOP SHOUTING ! ! ! !

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Voltage Factor for CVT

09/17/2012 9:31 AM

i) If the system is solidly earthed, then there could be power frequency overvoltage to the tune of 1.5 times the highest system voltage, during a single-line-to-earth fault, depending upon the fault loop impedance.

ii) If the system is impedance earthed, then during a single-line-to-earth fault, the overvoltage could be 1.9 times the HSV.

If you want to know the calculations, pl. enrol for our training programme on earthing.

Register to Reply