09/15/2012 3:13 AM
The value for voltage factor depending on earth system. Why rely on determining the type of earthing sysem
Pathfinder Tags: SHORT TIME V. FACTOR
Re: VOLTAGE FACTOR FOR CVT
09/15/2012 9:02 AM
Good Answers: 181
Re: Voltage Factor for CVT
09/15/2012 1:59 PM
STOP SHOUTING ! ! ! !
Good Answers: 170
09/17/2012 9:31 AM
i) If the system is solidly earthed, then there could be power frequency overvoltage to the tune of 1.5 times the highest system voltage, during a single-line-to-earth fault, depending upon the fault loop impedance.
ii) If the system is impedance earthed, then during a single-line-to-earth fault, the overvoltage could be 1.9 times the HSV.
If you want to know the calculations, pl. enrol for our training programme on earthing.