Dear All,
If we have effective grounding system (solidly), the factor voltage for capacitor voltage transformer must be 1.5/30S. The question is (if we use voltage factor 1.5/1.9 instead of 1.5/30S, will that be effective?) & what do we mean by values (1.5/30S --- 1.9/30S --- 1.9/8 hours)
Please I need to answer very
Thanks for all
Pathfinder Tags: Vf for CVT
Re: Is that will be effective
09/15/2012 9:00 AM
Good Answers: 181
Re: Effective Grounding
09/15/2012 2:08 PM
Sorry, the homework answering service is off line.
Good Answers: 170
09/17/2012 9:28 AM
First of all your specifications are incorrect. If the system is solidly earthed, then the voltage factor for a voltage transformer conencted in Star is 1.2 Continuous & 1.5 for 30 seconds.
If the system is impedance earthed with automatic tripping arrangement for the first earth fault, then this is 1.2 continuous & 1.9 for 30 seconds.
If the system is impedance earthed but with no interruption for the first earth fault, then the VT overvoltage factor is 1.2 continuous & 1.9 for 8 hours.